Is the damper supposed to be there?
andresloaiza
andresloaiza Member Posts: 3
    Steamhead Member Posts: 18,187
    If you mean the barometric draft regulator (swinging disc), yes.
    Consulting
    andresloaiza
  • andresloaiza
    I haven’t seen any other boiler with it so close. Right out of the combustion chamber
  • STEVEusaPA
    It would be better on the horizontal piece of flue pipe.
    HVACNUTkcopp
    pecmsg Member Posts: 6,767
    Do you have other pictures? I’m curious what the piping looks like.
    HVACNUT Member Posts: 7,216
    Agree it should be moved to the horizontal run. There's no way a combustion test is getting done without picking up free air from the regulator.
  • andresloaiza
    EdTheHeaterMan Member Posts: 11,555
    edited May 2022
    In the current location, the barometric draft regulator will work fine. However I also see a problem with getting proper combustion test results. It's easy enough to move it to the horizontal section of the vent connector
    We have a few like that- if you tip your analyzer probe down so it's below the barometric, you'll get good readings.
    The only drawback I see is that on some boilers, more noise will escape if the barometric is that close.
    Consulting
  • pedmec
    pedmec Member Posts: 1,238
    i would worry more about that near boiler piping than that damper location. bullhead tee on the equalizer and undersize. doesn't look like 1-1/2 as required by manufacturer unless pic is deceiving