Lochinvar boiler whb110n lockout mode
HeatingHelp
Administrator Posts: 722
This discussion was created from comments split from: Lochinvar Knight KB106 boiler. Lockouts from Temp Diff.
I have a lochinvar boiler whb110n that goes into lockout mode regularly a day an seems to clear it’s self..But sometimes I have to hit the reset button it’s always says fail ignition flam0
ARHL(Automatic Reset High Limit) which resets when the temp in the boiler cools down. MRHL(Manual Reset High Limit) requires a hands on reset even when boiler temps cools down.
These can be adjusted in the installer programing as well as the offset.
I just downloaded this service manual the other day. The installer didn't leave any documentation with the boiler. I printed it out and am going to leave it with the customer for the next tech.
Look at page 40 & 41 in the service manual-models 81-286.
https://www.manualsdir.com/manuals/163342/lochinvar-knight-heating-boiler-81-286.html
Changes can be made in the installer programing. The manual will tell you how to access the programing mode. You can look at the perimeters set for your unit and report those.
Most often it is a flow issue as a result of piping, including pumps. Less so a programing issue.
You can lookup anti-cycling in the manual, too, under troubleshooting.
Did you have a combustion analysis done on your boiler. If so you should have a printed receipt showing the combustion perimeters. Is your boiler on NG or Propane?
Using a flash on your camera for your pics would greatly enlighten things.0 -
JUGHNE, I don't understand, what am I missing? OH! Read all of Gater's post again and I get it, the sensor was the issue. I'm missing the ignition failure. I guess I'm getting ,too old. How in heck am I reading posts that are two days older than Moses?
Oh! I see, curt1schroeder, miss posted. I'm going to take an aspirin and go to bed.
@curt1schroeder
Do you see what happens when you post on top of old posts? Now poor @HomerJSmith needs to go to bed and will miss his Sunday evening routine
Albert Einstein4 -
President
HeatingHelp.com0 -
Most likely the flame rod needs cleaned. You can read what the flame rod current is on the display panel by scrolling through the menus. I don't remember what the lower reading should be before it shows an error, but it seems like most of the ones I have checked are reading around 11microamps, so if it seems really low, then that is probably the issue.
Rick0
- 50 Industry Classes
