Wiring a 2 zone valve to and 2 thermostat to a taco 2 zone switch relay
acura22itr
Member Posts: 11
Hey fellas
how do i hook this current system to a taco 2 zone switching relay so each floor / zone run independently ? Please help me i don’t know where the Honeywell zone valve wires go!
how do i hook this current system to a taco 2 zone switching relay so each floor / zone run independently ? Please help me i don’t know where the Honeywell zone valve wires go! 0
The yellow leads are the motor; the Red leads are the end switch.
IF you have a Taco ZVC panel, the yellow leads go to terminals 1&2 and the Red go to terminals 3&4.Bob Boan
I just noticed that you have two pumps, so why did you install two zone valves?
If you have a Taco SR502 PUMP panel, you can’t connect the zone valve directly to it since it’s 120v and the valves are 24v. You would need two 24v transformers or two relays.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.2 -
So bob boan to get this thing running . I need to not use the taco 2 zone switching panel n just use transformers instead ?0
Please answer my question why you installed the zone valves?Bob Boan
It appears that you installed the incorrect valves in order to properly zone your heating system. Since you obviously have 2 circulators, the proper valve woulds have been a Taco Sweat Check or Flow Check valve on each supply pipe.
Your other choice would be to use only one circulator and two zone valves. As it stands, you have two circulators (that require 120 Volts to operate) and two zone valves (that require 24 volts to operate).
You can make this work but it is sort of silly. Here is the diagram you will need to use and you will need to add two separate 24 volt transformers (one for each zone valve) in order to make this work.
In this diagram the zone valves will act as flow check valves. When there is a call for heat from one thermostat, the corresponding circulator and zone valve will open. The Red wires on the zone valves are not used in this case. This is the best I could come up with under the circumstances.
If you want to get rid of one of the circulator pumps and change the control to a ZVC 403 zone relay it would be easier to follow, but that involves repiping and you probably don't want to do that.
Look in this booklet to see the way you should have completed this for future reference. http://media.blueridgecompany.com/documents/ZoningMadeEasy.pdf Page 9 tells you about Flow Valves and page 15 explains zone valves.
Thanks so much @ Ed the heater man . I was YouTubing thinking i knew what to do . I was wrong . Happy ya pointed me in the right direction . @ bob i was googling and thinking this was the way but i was wrong0
Re- Ed's diagram:
If the tstat connections on the controller supply 24v, could he instead wire each zone tstat in series with the corresponding zone valve ? When the tstat closes, the zone valve gets power. Or would that be too much resistance for the controller to sense a zone call ?30+ yrs in telecom outside plant.
Currently in building maintenance.0 -
You need to keep the transformer on the zone panel separate from the transformer for the zone valves.Dave Carpentier said:Re- Ed's diagram: If the tstat connections on the controller supply 24v, could he instead wire each zone tstat in series with the corresponding zone valve ? When the tstat closes, the zone valve gets power. Or would that be too much resistance for the controller to sense a zone call ?
If you use one 24v 40va transformer to power the zone valves through the thermostats, and wire the end switches (red wires) to RW on the panel, the transformers are isolated from each other.
In Ed's diagram, the circulator and zone valve get powered at the same time, but it will take a few seconds for the zone valve to open. That might cause a little hammering.
Get those CO detectors yet?2 -
Yes i got the CO DETECTORS . I just bought this house so I’m doing the work myself . I don’t know why they by passed the spill switch . I’ll buy a new one n connect it0
Ok thanks I’ll go to Home Depot and get the things0
One other thing: is that regular plumbing PEX that you used?Bob Boan
I strongly advise getting a Low Level CO Detector. The UL Approved detectors need to reach and maintain 70 PPM for up to 3 hours before alarming. Low level alarms like the Defender alert at 15PPM within 60 minuets.acura22itr said:Yes i got the CO DETECTORS . I just bought this house so I’m doing the work myself . I don’t know why they by passed the spill switch . I’ll buy a new one n connect it
https://www.trutechtools.com/Defender-LL6170-Low-Level-Carbon-Monoxide-Monitor-Alarm#:~:text=A direct replacement for the LL6070. ,within 15 minutes 5 more rows0 -
Usually not, there is a relay somewhere on the boiler jacket or aquastat if you have one.
Your boiler model # would be helpful.0 -
Ok I’ll look up the model number n google it thanks guys0
Looks like a roughly twenty year old Weil McLain CG. See attached electrical schematic on page 4. On most models around that time frame there would be a circulator relay almost directly behind the emergency switch. The relay takes a 24 volt signal from the thermostat circuit and closes the plug in relay. The end result is this relay sends 120 volts to the circulator pump.
https://www.weil-mclain.com/sites/default/files/field-file/cg-series-12-gas-control-supplement_1.pdf
Thanks a lot @ScottSecor you was very helpfull0
Hey guys here is a more better pic of my well McClain boiler with pic of the relay ( in back of the cut off switch ) where does the pump connect to on this ? You can see the hot wire , neutral wire , yellow wire and another black ., please help me
I'm in the dark here. The pump should only run when there is a call for heat. Do you have some kind of schematic that you can post? What are you going by for wiring the system?0
@Erin Holohan Haskell, Please help. @acura22itr has 4 discussions about the same problem. Can you merge?
I've merged all of the posts here. Thanks!EdTheHeaterMan said:@Erin Holohan Haskell, Please help. @acura22itr has 4 discussions about the same problem. Can you merge?
President
HeatingHelp.com0
- 76 Pipe Deterioration