Utica steam
Snowmelt
Member Posts: 1,457
Installing a 4 section residential steam boiler. I just hung up the phone with technical support. I’m using both risers. Technical told me to keep it two inch, after the tee going to the supply I could bump it up to 4 inch with a 2 - 4 reducer that’s what the original system is.
Post the boiler nameplate.
I’m sorry it was Utica 150,000 btu out0
Is this "Utica Boiler" or "Utica Heating"?
They're not the same..............All Steamed Up, Inc.
Consulting0 -
I’m sorry that was the old boiler which was a peerless0
Post the actual model number if you have it
Peg 150 tomorrow I start the job . I don’t think I will do a drop header but I will you two taps0
Utica Boiler. Side outlets are 2" rather than 2-1/2".All Steamed Up, Inc.
Consulting0 -
PSB 5 D , I’m planing on using both risers I drew a little diagram
Pretty sure the PSB series is a Dunkirk
John Pughe0 -
It is. And the instructions clearly say DO NOT reduce the size of the steam tappings. That technical support person clearly can't read.Pughie1 said:Pretty sure the PSB series is a Dunkirk
John Pughe
I'd build a standard 2-1/2" drop header, using both risers and dripping into the equalizer as usual, and run the takeoff from that into the existing 4" header, dripping that below the waterline into the return before the Hartford Loop. This will give you some nice, dry steam.All Steamed Up, Inc.
Consulting0 -
Steam head so just pipe it as I see it………planing on going 24 inch with risers then make the mains 4 inch, just won’t be pretty I will do the best I can0