Utica steam
Snowmelt
Member Posts: 1,425
Installing a 4 section residential steam boiler. I just hung up the phone with technical support. I’m using both risers. Technical told me to keep it two inch, after the tee going to the supply I could bump it up to 4 inch with a 2 - 4 reducer that’s what the original system is.
0
Comments
-
Post the boiler nameplate.
0 -
I’m sorry it was Utica 150,000 btu out0
-
Is this "Utica Boiler" or "Utica Heating"?
They're not the same..............All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
I’m sorry that was the old boiler which was a peerless0
-
Post the actual model number if you have it
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Peg 150 tomorrow I start the job . I don’t think I will do a drop header but I will you two taps0
-
Utica Boiler. Side outlets are 2" rather than 2-1/2".All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
PSB 5 D , I’m planing on using both risers I drew a little diagram
0 -
(
0 -
Pretty sure the PSB series is a Dunkirk
John Pughe0 -
It is. And the instructions clearly say DO NOT reduce the size of the steam tappings. That technical support person clearly can't read.Pughie1 said:Pretty sure the PSB series is a Dunkirk
John Pughe
I'd build a standard 2-1/2" drop header, using both risers and dripping into the equalizer as usual, and run the takeoff from that into the existing 4" header, dripping that below the waterline into the return before the Hartford Loop. This will give you some nice, dry steam.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Steam head so just pipe it as I see it………planing on going 24 inch with risers then make the mains 4 inch, just won’t be pretty I will do the best I can0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements