5/8 tubing on 6" centers

Hey everyone what is the best way to practically lay out 5/8 tubing on 6" centers.

Web says max radius is 6" for 5/8. Do I just let the 180 turns flair out?

Layout and heat load done by Rehau. 

Tubing is Uponor hePEX and will be attached to 6" wire mesh in 4" concrete.

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • hot_rod
    hot_rod Member Posts: 25,141
    Yes, you will have to “light bulb” the ends of the loops to get a tight spacing like that
    why .5/8? Just to get long loop lengths?
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    Rich_49
  • mattmia2
    mattmia2 Member Posts: 12,887
    why not interleave 2 tubes at 12"?
  • yotakrawler
    yotakrawler Member Posts: 5
    Thanks that is a good idea. I am having a hard time picturing how that would work in a room that is a single zone and a single loop. Would the tube cross over itself? If they do cross over, what are your thoughts on the chair height for my wire mesh? Right now I am planning for 2 inch which give me 1.25 inch of concrete above the tubing. If have to stack the tube that only leaves about. 5 inches. I could get 1.5 inch chairs.
  • yotakrawler
    yotakrawler Member Posts: 5
    hot_rod said:
    Yes, you will have to “light bulb” the ends of the loops to get a tight spacing like that
    why .5/8? Just to get long loop lengths?
    Yeah, pushing 400ft in some places.
  • hot_rod
    hot_rod Member Posts: 25,141
    No harm in "over tubing" I'd consider two 200 '1/2" loops instead of a 350' 5/8".
    More tube= lower SWT options, faster recovery, more even surface temperature.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    Zmanrick in Alaska
  • mattmia2
    mattmia2 Member Posts: 12,887
    I was thinking some sort of staple up. I will defer to others on how to handle crossing over in concrete. 2 parallel loops would reduce your loop length and might get you a smaller tubing size(although it would use a bit more tubing overall)
  • yotakrawler
    yotakrawler Member Posts: 5
    Unfortunately at this point I have materials in hand and will probably have to make this configuration work. Any thoughts on what would be better "light bulb" or crossing over?

    hot_rod said:
    No harm in "over tubing" I'd consider two 200 '1/2" loops instead of a 350' 5/8". More tube= lower SWT options, faster recovery, more even surface temperature.
    mattmia2 said:
    I was thinking some sort of staple up. I will defer to others on how to handle crossing over in concrete. 2 parallel loops would reduce your loop length and might get you a smaller tubing size(although it would use a bit more tubing overall)

  • GGross
    GGross Member Posts: 1,504
    If you know anyone in your area that might have a pexgun wire tie tool to lend you they are super nice for tieing down to wire mesh.

    I think I would "light bulb" personally. Normally I would have used 1/2" tube 9" on center, but more tubing is generally better, and I can't fault you for trying to do something better than average
  • hot_rod
    hot_rod Member Posts: 25,141
    There are other tube layouts some of these would only have one "light bulb" :)r
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    mattmia2
  • TAG
    TAG Member Posts: 792
    I would just go around the room ... that's how I did a big sunroom w/ lots of windows. In my case I did two loops that sit inside inside one other -- but one loop is just as easy. In a big space I like the loop around vs up down/ back forth.
  • yotakrawler
    yotakrawler Member Posts: 5
    Thanks for the feedback everyone. I am attempting to do radiant cooling and that is the reason for the 6"spacing and the 5/8 tubing. My understanding is that cooling needs higher flow rates to maintain a lower delta T and the larger tubing keeps the pump sizes in check.