5/8 tubing on 6" centers
yotakrawler
Member Posts: 5
Hey everyone what is the best way to practically lay out 5/8 tubing on 6" centers.
Web says max radius is 6" for 5/8. Do I just let the 180 turns flair out?
Layout and heat load done by Rehau.
Tubing is Uponor hePEX and will be attached to 6" wire mesh in 4" concrete.
Web says max radius is 6" for 5/8. Do I just let the 180 turns flair out?
Layout and heat load done by Rehau.
Tubing is Uponor hePEX and will be attached to 6" wire mesh in 4" concrete.
0
Comments
-
-
why not interleave 2 tubes at 12"?0
-
Thanks that is a good idea. I am having a hard time picturing how that would work in a room that is a single zone and a single loop. Would the tube cross over itself? If they do cross over, what are your thoughts on the chair height for my wire mesh? Right now I am planning for 2 inch which give me 1.25 inch of concrete above the tubing. If have to stack the tube that only leaves about. 5 inches. I could get 1.5 inch chairs.0
-
hot_rod said:Yes, you will have to “light bulb” the ends of the loops to get a tight spacing like that
why .5/8? Just to get long loop lengths?0 -
-
I was thinking some sort of staple up. I will defer to others on how to handle crossing over in concrete. 2 parallel loops would reduce your loop length and might get you a smaller tubing size(although it would use a bit more tubing overall)0
-
Unfortunately at this point I have materials in hand and will probably have to make this configuration work. Any thoughts on what would be better "light bulb" or crossing over?hot_rod said:No harm in "over tubing" I'd consider two 200 '1/2" loops instead of a 350' 5/8". More tube= lower SWT options, faster recovery, more even surface temperature.mattmia2 said:I was thinking some sort of staple up. I will defer to others on how to handle crossing over in concrete. 2 parallel loops would reduce your loop length and might get you a smaller tubing size(although it would use a bit more tubing overall)
0 -
If you know anyone in your area that might have a pexgun wire tie tool to lend you they are super nice for tieing down to wire mesh.
I think I would "light bulb" personally. Normally I would have used 1/2" tube 9" on center, but more tubing is generally better, and I can't fault you for trying to do something better than average0 -
There are other tube layouts some of these would only have one "light bulb" :)rBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
I would just go around the room ... that's how I did a big sunroom w/ lots of windows. In my case I did two loops that sit inside inside one other -- but one loop is just as easy. In a big space I like the loop around vs up down/ back forth.0
-
Thanks for the feedback everyone. I am attempting to do radiant cooling and that is the reason for the 6"spacing and the 5/8 tubing. My understanding is that cooling needs higher flow rates to maintain a lower delta T and the larger tubing keeps the pump sizes in check.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements