Steam sq ft, if not listed on steam boiler
BirchLeaf
Member Posts: 56
Is there a way to determine the steam sq. ft. of a steam boiler if it's not listed on the plate/sticker (by using other numbers listed)?
(I wrote down everything that was listed.)
BTU can be converted. Send a pic of the panel?
@ethicalpaul
The boiler is gone (didn't take pic.) I wrote everything down, though.
Input BTU per hr.: 112,500
Heating capacity BTU/hr.: 90,000
Is this the same boiler from your other thread that you listed as rated for 321 sq ft?1
If this is a Utica, Columbia or one of the Dunkirk boilers that might have any one of several names, it's 281 to 292 square feet.BirchLeaf said:@ethicalpaul
Heating capacity BTU/hr.: 90,000All Steamed Up, Inc.
Consulting2 -
With the 90,000 that would be with pick up factor, so the actual rating would have been what Steamhead said @281 sq ft
90,000=375 EDR
375/1.33=2812 -
You guys are amazing. Thank you all so much!
@Steamhead You're right! Certified by Dunkirk Radiator Corp. It said installed in 1985, it ran wonderfully, I loved it, and I bet it could have been repaired.0 -
- 87.1K THE MAIN WALL
- 58 Biomass
- 114 Chimneys & Flues
- 110 Geothermal
- 162 Indoor-Air Quality
- 71 Pipe Deterioration
- 393 Solar
- 55 Water Quality
- 46 Industry Classes
