Dunkirk quantum 90 not staying Lit
wilson95
Member Posts: 5
I have a dunkirk quantum 90 it runs through the cycle fine then when it get to light only lights for one second then shuts off and starts the cycle over I installed a new Igniter and air flow switch I and get it to stay lit only if I put a jumper wire on the air flow switch
if your able to get it running by jumping the air switch I would guess you have either a blockage of your exhaust or air inlet piping or a partially clogged heat exchanger . Just as a wag but I would gather that unit has a few years on it ?I do hope if your operating it w a jumper that you have a co dect in the boiler room and main living area . When was the last time the unit received a proper servicing and combustion testing ? Peace and good luck clammy
R.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
My exhaust and intake pipes are clear0
You’re condensate drain is clogged.Bob Boan
I cleaned it out still tuning the same cycle0
@wilson95
take the tubing off the air flow switch and make sure it's clean. You should have it checked and serviced.
You either have a bad switch or something is plugged or you combustion is way off0 -
Did you clean the condensate trap and the sediment trap at the bottom of the exhaust pipe?Bob Boan
Yep and I cleaned every pipe out0
Did you ever figure this out?