Dunkirk quantum 90 not staying Lit
wilson95
Member Posts: 5
I have a dunkirk quantum 90 it runs through the cycle fine then when it get to light only lights for one second then shuts off and starts the cycle over I installed a new Igniter and air flow switch I and get it to stay lit only if I put a jumper wire on the air flow switch
0
Comments
-
if your able to get it running by jumping the air switch I would guess you have either a blockage of your exhaust or air inlet piping or a partially clogged heat exchanger . Just as a wag but I would gather that unit has a few years on it ?I do hope if your operating it w a jumper that you have a co dect in the boiler room and main living area . When was the last time the unit received a proper servicing and combustion testing ? Peace and good luck clammy
R.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
Specializing in steam and hydronic heating0 -
My exhaust and intake pipes are clear0
-
You’re condensate drain is clogged.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
I cleaned it out still tuning the same cycle0
-
@wilson95
take the tubing off the air flow switch and make sure it's clean. You should have it checked and serviced.
You either have a bad switch or something is plugged or you combustion is way off0 -
Did you clean the condensate trap and the sediment trap at the bottom of the exhaust pipe?Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Yep and I cleaned every pipe out0
-
Did you ever figure this out?
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements