Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Dunkirk quantum 90 not staying Lit

Options
I have a dunkirk quantum 90 it runs through the cycle fine then when it get to light only lights for one second then shuts off and starts the cycle over I installed a new Igniter and air flow switch I and get it to stay lit only if I put a jumper wire on the air flow switch 

Comments

  • clammy
    clammy Member Posts: 3,111
    Options
    if your able to get it running by jumping the air switch I would guess you have either a blockage of your exhaust or air inlet piping or a partially clogged heat exchanger . Just as a wag but I would gather that unit has a few years on it ?I do hope if your operating it w a jumper that you have a co dect in the boiler room and main living area . When was the last time the unit received a proper servicing and combustion testing ? Peace and good luck clammy
    R.A. Calmbacher L.L.C. HVAC
    NJ Master HVAC Lic.
    Mahwah, NJ
    Specializing in steam and hydronic heating
  • wilson95
    wilson95 Member Posts: 5
    Options
    My exhaust and intake pipes are clear 
  • Ironman
    Ironman Member Posts: 7,376
    Options
    You’re condensate drain is clogged.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • wilson95
    wilson95 Member Posts: 5
    Options
    I cleaned it out still tuning the same cycle 
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,524
    Options
    @wilson95

    take the tubing off the air flow switch and make sure it's clean. You should have it checked and serviced.

    You either have a bad switch or something is plugged or you combustion is way off
  • Ironman
    Ironman Member Posts: 7,376
    Options
    Did you clean the condensate trap and the sediment trap at the bottom of the exhaust pipe?
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • wilson95
    wilson95 Member Posts: 5
    edited February 2022
    Options
    Yep and I cleaned every pipe out