Dunkirk quantum 90 not staying Lit
I have a dunkirk quantum 90 it runs through the cycle fine then when it get to light only lights for one second then shuts off and starts the cycle over I installed a new Igniter and air flow switch I and get it to stay lit only if I put a jumper wire on the air flow switch
  • clammy
    clammy Member Posts: 3,247
    if your able to get it running by jumping the air switch I would guess you have either a blockage of your exhaust or air inlet piping or a partially clogged heat exchanger . Just as a wag but I would gather that unit has a few years on it ?I do hope if your operating it w a jumper that you have a co dect in the boiler room and main living area . When was the last time the unit received a proper servicing and combustion testing ? Peace and good luck clammy
    R.A. Calmbacher L.L.C. HVAC
    NJ Master HVAC Lic.
    Mahwah, NJ
  • wilson95
    wilson95 Member Posts: 5
    My exhaust and intake pipes are clear
  • Ironman
    Ironman Member Posts: 7,886
    You’re condensate drain is clogged.
    Bob Boan
  • wilson95
    I cleaned it out still tuning the same cycle
    EBEBRATT-Ed Member Posts: 19,887
    @wilson95
    take the tubing off the air flow switch and make sure it's clean. You should have it checked and serviced.
    You either have a bad switch or something is plugged or you combustion is way off
  • Ironman
    Did you clean the condensate trap and the sediment trap at the bottom of the exhaust pipe?
    Bob Boan
  • wilson95
    edited February 2022
    Yep and I cleaned every pipe out
  • twistedmetal
    twistedmetal Member Posts: 2
    Did you ever figure this out?