Adding a low pressure gauge to my steam boiler
Looking to add a low pressure gauge to my pigtail. Picked up a black T and elbow and a few .5" nipples along with a 5PSI gauge.
Before I install, do you see any problems attaching this to where the pigtail goes?
Thanks so much,
Chris
As long as the pig tail is connected to the boiler no problem.0
In that location - before the pigtail loop - in case where the pigtail is clogged in the loop you would not be seeing the same pressure that the pressuretol is seeing. Mine is mounted off a T attached at the top of pigtail, between the pigtail and the pressuretrol. I also used brass fittings.
You would also want to protect the gauge from live steam hitting it, another reason mine is on the cold side (non-boiler side) of the pigtail loop.
3 -
@da13ear
I would use all brass fittings. I know they are more $$ Black is ok if you check it to make sure it's not plugged up from time to time.
I would put a 1/4" ball valve or petcock under the new gauge to save ware and tare on it. Keep it off and just open it when you check the pressure
jmho3 -
If you want to see very low pressure on that gauge, I would not put it on a pigtail, and I would not put it an that position. Mount it well above the top of the boiler instead.
As @ChrisJ noted on this thread: https://forum.heatinghelp.com/discussion/186629/can-you-balance-a-system-with-no-measurable-pressure-ever#latest if you put the gauge on the pigtail, it won't read very low pressures.
My low pressure gauge was formerly set up just like @Dan_NJ's-after the pigtail. It never read anything until the pressure began to rise just before a Pressuretrol shut-off (when recovering from setbacks). I recently moved it to a tee on the pressure relief valve with a long vertical riser, and now it reads 1" to 2" of water, when the boiler is steaming but not building pressure.
As for materials, I agree you should stay away from black. I've been using stainless steel as it is generally less expensive than brass.0 -
My gauge is 0-3 PSI range and I can see it dance around the first few tickmarks for the majority of cycles. I see no practical purpose in trying to read the first 1/2 or 1 oz of pressure (1-2" wc) on my plain vanilla one pipe system. If it were some kind of vapor/vacuum, 2 pipe arrangement that might be useful. In my case I really only care that it stays very low most of the time, and that it doesn't exceed my cutout when it does cycle on pressure.0
Hey guys,
Thank you all for the feedback. I picked up all the parts in brass as recommended. I couldn't get my hands on an 1/4 ball valve so I've put this on hold for the time being. Will revisit it next week and share some pictures.
One question I need to solve between now and then - the entire setup ends up being too big to spin onto the boiler without removing the low water cutoff. Any suggestions on how to get around that without removing the low water cutoff?
Pic attached for reference
Dunno. Works for me. But it does "bounce" a little. The black scale is oz/in2.Chris_L said:If you want to see very low pressure on that gauge, I would not put it on a pigtail, and I would not put it an that position. Mount it well above the top of the boiler instead.
As @ChrisJ noted on this thread: https://forum.heatinghelp.com/discussion/186629/can-you-balance-a-system-with-no-measurable-pressure-ever#latest if you put the gauge on the pigtail, it won't read very low pressures...
delcrossv said:
If you want to see very low pressure on that gauge, I would not put it on a pigtail, and I would not put it an that position. Mount it well above the top of the boiler instead. As @ChrisJ noted on this thread: https://forum.heatinghelp.com/discussion/186629/can-you-balance-a-system-with-no-measurable-pressure-ever#latest if you put the gauge on the pigtail, it won't read very low pressures...
Also what does that gauge say when the boiler is off?Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
Have you ever checked that gauge against a manometer? I'd be curious how closely they match at very low pressures--say 0-3 inches of water. (I am guessing not very if the gauge is on a pigtail.)delcrossv said:
Also, I'd be curious what folks think about the chance of water from the pigtail getting pushed into the gauge. I don't think capsule gauges like the OP's are designed for liquids. Note that the distributor describes his as a diaphragm "gas" gauge. (I think it is really a capsule gauge.)0 -
Goes to zero with the boiler off. My system operates at 4 to 8 oz, so I have no need to measure at 3" WC.Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.0
Thanks for the shoutout to my thread! So the 'long vertical riser' takes the place of the pigtail in keeping water out of the gauge? How long is 'tall'? I'd love to see anything on my 1-3 psi gauge. Do I need a oz/sq in gauge?Chris_L said:If you want to see very low pressure on that gauge, I would not put it on a pigtail, and I would not put it an that position. Mount it well above the top of the boiler instead.
Is there a Harbor Freight near you? https://www.harborfreight.com/14-in-full-port-ball-valve-63553.htmlda13ear said:I couldn't get my hands on an 1/4 ball valve so I've put this on hold for the time being.
Jells said:
If you want to see very low pressure on that gauge, I would not put it on a pigtail, and I would not put it an that position. Mount it well above the top of the boiler instead. As @ChrisJ noted on this thread: https://forum.heatinghelp.com/discussion/186629/can-you-balance-a-system-with-no-measurable-pressure-ever#latest if you put the gauge on the pigtail, it won't read very low pressures. My low pressure gauge was formerly set up just like @Dan_NJ's-after the pigtail. It never read anything until the pressure began to rise just before a Pressuretrol shut-off (when recovering from setbacks). I recently moved it to a tee on the pressure relief valve with a long vertical riser, and now it reads 1" to 2" of water, when the boiler is steaming but not building pressure. As for materials, I agree you should stay away from black. I've been using stainless steel as it is generally less expensive than brass.
It creates an air trap to block the steam. Air can't get out so steam can't get in.
You'll need to choose a gauge with the range you need. I'd recommend a Dwyer Magnehelic. Something with a 4" range +-Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
I'd recommend that. 0=3 psi gauges are IMO too large a range . Most well tuned steam systems run at 8 ounces or less.Jells said:
Supply house has Winters ounce gauges for a lot less than a Magnehelic, ( unless you're measuring low inches of WC pressures- and you don't know that yet.)Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.0 -
I'd recommend that. 0=3 psi gauges are IMO too large a range . Most well tuned steam systems run at 8 ounces or less. Supply house has Winters ounce gauges for a lot less than a Magnehelic, ( unless you're measuring low inches of WC pressures- and you don't know that yet.)
First they tolerate water.
Second even a 2" Magnehelic will not be damaged by as much a 15 psi.
They are a better gauge and will last longer and take more abuse. They can almost always be found on eBay for $30-50.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
cross_skier said:@ChrisJ
Any issues mounting the Magnehelic gauge? I doesn't look like other gauges with npt threads
They have two sets of holes, I think 1/8 npt female.
I say sets because they have negative pressure connections and well as positive depending on what you want to measure.
Since there's 2 of each you plug the one you're not using. The new gauges come with plugs.
They are aluminum with would do better with steel connections but I used brass and I'm sure one day I'll pay for it.
2 -
Isn't 1 ounce of pressure = 1.7 inches w.c.?delcrossv said:Goes to zero with the boiler off. My system operates at 4 to 8 oz, so I have no need to measure at 3" WC.
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes1 -
@Jells wrote:
With the riser and fittings, my gauge is about a foot above the top of the boiler and 2 feet above the water line. Since the pipe to it never gets hot, I presume steam never reaches it.Jells said:
See below. (I need to put the case back on it.):
The scale on this is 0-10" of water. (It is a gas manifold gauge I found on eBay.) If you want to see what pressure you operate at, I'd suggest a simple manometer like the one below. Just put a hose barb on the valve at the bottom of your sight glass and attach some tubing to measure the pressure. Though you can't see it very well in the picture, the pressure in inches of water is just the distance between the water level in the sight glass and tubing in inches.
But do this carefully! The open end of the tubing should be near the ceiling, and be sure to turn the valve off well before the water rises that high (roughly 2 psi depending on your ceiling height and boiler) so you don't get a hot shower. Keep the valve the hose barb is attached to closed when not reading the water column.
Chris_L said:If you want to see what pressure you operate at, I'd suggest a simple manometer like the one below. Just put a hose barb on the valve at the bottom of your sight glass and attach some tubing to measure the pressure. Though you can't see it very well in the picture, the pressure in inches of water is just the distance between the water level in the sight glass and tubing in inches. But do this carefully! The open end of the tubing should be near the ceiling, and be sure to turn the valve off well before the water rises that high (roughly 2 psi depending on your ceiling height and boiler) so you don't get a hot shower. Keep the valve the hose barb is attached to closed when not reading the water column.0
@EBEBRATT-Ed is it ok to put a union between the pigtail and the presuretrol? Just trying to stick to the best practices.
@Hap_Hazzard I do! Thanks so much for the feedback.
Hint hint
https://www.ebay.com/itm/175028297960?epid=7046120044&hash=item28c07fe0e8:g:QlwAAOSw0aNhltivSingle pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
Thanks, I happened to pick up one this morning0
It also seems Home Depot has them in the air tools dept, not in plumbing.Hap_Hazzard said:
https://www.homedepot.com/p/Husky-1-4-in-Full-Port-Ball-Valve-HDA70100AV/1000399011 -
@ChrisJ. Would a stainless reducing nipple 1/4-1/8 work well between the gauge's aluminum case and the brass plumbing?
https://www.ebay.com/itm/292369195531
@da13ear
Well if you can't spin it put a union there. You don't have another choice unless you pipe it above the boiler jacket0 -
90% sure that would be far worse into aluminum than brass.cross_skier said:@ChrisJ. Would a stainless reducing nipple 1/4-1/8 work well between the gauge's aluminum case and the brass plumbing?
Steel is much better than both, SS might be the worst.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
I have one on mine. I got tired of having to disconnect the wires.da13ear said:@EBEBRATT-Ed is it ok to put a union between the pigtail and the presuretrol? Just trying to stick to the best practices.
Is all sched 40 SS pipe and fittings 300-series stainless?ChrisJ said:90% sure that would be far worse into aluminum than brass.
Steel is much better than both, SS might be the worst.Just another DIYer | King of Prussia, PA
I went with a carbon steel reducing nipple between my brass plumbing and the aluminum gauge. I would post the link but it hasn't arrived. Gauge is great, got a killer deal on a new gauge like @ethicalpaul's. Two left if interested. --
https://www.ebay.com/itm/143917746131
@Chris_L I did the tube from the bottom of the sight glass. No pressure. But my heat guy says it's not a valid way to measure steam pressure! He's well thought of here, but my gut says he's wrong. Pressure is pressure, whether you tap it below the waterline or above. How do I convince him?0
Introduce him to Archimedes.Jells said:How do I convince him?
Why didn’t you include the original 30psi gauge to meet code?Dan_NJ said:In that location - before the pigtail loop - in case where the pigtail is clogged in the loop you would not be seeing the same pressure that the pressuretol is seeing. Mine is mounted off a T attached at the top of pigtail, between the pigtail and the pressuretrol. I also used brass fittings.
You would also want to protect the gauge from live steam hitting it, another reason mine is on the cold side (non-boiler side) of the pigtail loop.0 -
The original 30 psi gauge is there per code, out of frame. Still connected directly to the boiler end section via its tapping, and probably to this day still reading 5 psi 24/7/365 (I would confirm for you except I've been out of that place for some time).0
- 110 Chimneys & Flues
- 981 Plumbing
- 387 Solar
- 17 Recall Announcements