Mgb 095k thermostat wiring
tomf1035
tomf1035 Member Posts: 3
Trying to wire a utica mgb95 the diagram calls for c, tw, and tr thermostat wires i can find no reference to which wire is which. Also my thermostat only has two wires.  Any help?
    EBEBRATT-Ed Member Posts: 20,165
    If your thermostat has only 2 wires and doesn't need a "C"-Common' wire on the thermostat end you should have a wire on R or Rh and the other wire on W.
    On the boiler end one wire should go to TW & the other one to TR . But don't forget your limit controls and safety controls may need to be in that circuit.
    Follow the MFG wiring diagram & make sure all the limits and safety's work.
    Is this a new install??
    Jamie Hall Member Posts: 27,359
    The manual for your boiler -- there are about 10 different variations -- will have the correct wiring diagram. Usually the only two wires you need are tw and tr, and if it is a two wire thermostat, it doesn't matter which is which. If it is a fancy three wire thermostat, you will have to locate a common for the c wire on the boiler somewhere.
  • tomf1035
    It is a new install. The boiler has a spot for a c wire so does the thermostat but your saying i probably don't need it?
  • tomf1035
    Do you think i could just tie the tw and tr together and control the heat with the zone valve?
  • Zman
    Zman Member Posts: 7,609
    Are you saying you only have 2 wires running from the t-stat and boiler but your thermostat has 3 terminals?
    Albert Einstein
    At a guess, if you tie TR and TW together the boiler will never shut off. You will have no control at all.
  • Ironman
    Ironman Member Posts: 7,903
    What zone valve do you have? You make it sound as though there’s only one. Is that correct?
    Bob Boan
    EdTheHeaterMan Member Posts: 12,159
    edited November 2021
    I believe that you are looking at this diagram @tomf1035
    I can see the C TR and TW indicated on the thermostat in the upper left of the diagram. (outlined in red)
    This is how you would connect a 2 wire thermostat