Honeywell VisionPro TH8321R1001 Stat Question
tribemaster
Member Posts: 8
Here's a current pic of the wiring on my stat. It now recognizes the outdoor sensor and the aux heat kicks in at 39 degrees. I came home yesterday and the stat was set to 68 but the temp on the stat read 66. I have to raise the temp up to 72 or 73 for the heat pump to kick on -- kind of a head scratcher. Should I install a more robust jumper between RC and R? Any suggestions?
The outdoor sensor is within a degree or so -- not sure of the brand. I have a HP with LP gas furnace.0
There is a jumper between RC and R. HP doesn't run if I place the red wire in R -- so I installed it in RC.0
Has it ever worked right? As long as the jumper's in place, it shouldn't matter which terminal the red wire goes to.
There are a number of set points that have to do with changeover from HP to furnace. Have you checked them?
The only set point I noticed was the switch over once the outside temp drops below 40 degrees. Are there others I should look at?0
I found a comprehensive manual for the 8000 series, attached. Go through the heat pump section on page 78 & check your settings.
Is this a new thing that it didn't do before?
It was happening with the A/C over the summer. I had a new HVAC system installed in Feb 2020 and have had issues with the 3 previous stats that were installed. My HVAC guy was suppose to install the 4th stat last month and ghosted me (he gave me a 3-year labor warranty BTW - which means nothing if it isn't honored), so I'm muddling thru these issues on my own. I do appreciate all the assistance and will make these changes tonite when I get home. Just want to check one more thing -- I have a HP w/gas furnace backup -- so should have 1 cooling stage and 2 heating stages -- is this correct? Thanks again -- this forum has been awesome!!!0
One HP stage (compressor) & one aux/backup stage (propane furnace). It's important to tell the stat it's a dual-fuel setup, you don't want the furnace to come on during HP operation, defrost or otherwise.
I've got a similar setup I'm responsible for (HP over gas furnace), I'll double check the settings after work today & tell you what they're set at. I'm pretty sure it handles changeover (HP<->furnace) correctly, but I'm not there all the time.
I did program the stat for dual-fuel. Thanks for your help!0
It's 1 stage cooling & 1 stage heat. Made the change you suggested -- working well so far!0
Great. Does it try to heat with the HP (when conditions are acceptable)?0
Yes it does and switches to Aux Heat when temp drops below 40. Thanks again for the assistance!0
- 87K THE MAIN WALL
- 115 Chimneys & Flues
- 106 Geothermal
- 982 Plumbing
- 388 Solar
