Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Vaporstat Model

Options
I have read past posts on vaporstat with range of 16oz max, If I want cut in at .5 psig (8oz) and cut out at 1.5 psig (24 oz) how do I do that with a 16 oz max vaporstat?
Can anyone recommend a vaporstat model for .5/1.5 psig? If not how about a pressuretrol model and best place to get one?

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 23,330
    Options
    For that pressure range you need the 0 to 4 psi vapourstat. L408J1017
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • mattmia2
    mattmia2 Member Posts: 9,677
    Options
    Let's back up and ask why you want to run it that high?