Un-Insulated Steam Pipe Issue
More pictures.
That will help I am sure. Just make sure that everything is well pitched before you close it up.
I am suspicious of not having enough pitch on the runout to the radiator and my reason is that the riser going through the floor up to the radiator only has 1 elbow, no swing joint which tells me the horizontal pipe is basically flat. Check the pitch of the radiator also.
I would hate to see you close it up after all that work and not have it fixed.
Insulation is good. But I predict your problem will remain. I had 3 radiators supplied by 1” pipe in uninsulated exterior walls and they supplied fine.
I suspect you might have incorrect near boiler piping that is causing water to be thrown up into the main and to the kitchen radiator.NJ Steam Homeowner.
They just 45'd it at that main. It does have a continuous downward pitch. I pitched the radiator good last year. Will double check. I made the cover removable with thread inserts into the framing so if I do have to remove its 5 screws and I have access. I was thinking how I don't want to have to take this all apart again. Her is a pic of the pipe before I insulated it.EBEBRATT-Ed said:That will help I am sure. Just make sure that everything is well pitched before you close it up. I am suspicious of not having enough pitch on the runout to the radiator and my reason is that the riser going through the floor up to the radiator only has 1 elbow, no swing joint which tells me the horizontal pipe is basically flat. Check the pitch of the radiator also. I would hate to see you close it up after all that work and not have it fixed.
I'll throw pictures below of the near boiler piping before and after insulation. I do believe the header should have been larger than two inches and it probably would have helped if they used both ports to run the two lines out instead of one. The dining room radiator (the one I'm having issues with) is the first radiator off the line going to the right and the kitchen radiator is the first off the line going to the left. I have no issues with the kitchen radiator and it heats great. They are about equal distance down the line. The only difference being the kitchen one is insulated all the way to the radiator so that is what lead me to believe the insulation was the issue, although I did wonder if it could be wet steam. Let me say that this wasn't just an uninsulated wall cavity that still has the heat of the house on one side of the wall and then board insulation and siding on the other side providing some sort of insulation. There was maybe 1/2 crumbling particle boarding looking wood right up against the pipe and that was all between the pipe and outside. I hope this fixes it and I guess trial and error is the only way to know haha. I always appreciate your input.ethicalpaul said:Insulation is good. But I predict your problem will remain. I had 3 radiators supplied by 1” pipe in uninsulated exterior walls and they supplied fine.
I would open that bay to the basement. Much less chance of freezing. Insulate the outside cover.
Why do they notch floor Joyce like that? Consider sistering up or at least some plywood bolted and glued where those notches are.0 -
I had thought about leaving it open. The coldest the basement gets is in the 40s so I figured it wouldn't have much chance of freezing with it open. I imagine with the notches it was just piss poor planning when initially installing. Should have installed the main slightly lower or came up with a different idea for running the pipe. I will definitely sister it. Thanks!pecmsg said:I would open that bay to the basement. Much less chance of freezing. Insulate the outside cover. Why do they notch floor Joyce like that? Consider sistering up or at least some plywood bolted and glued where those notches are.0 -
My house, as well as many others I've been to have the joists notched around steam piping.pecmsg said:I would open that bay to the basement. Much less chance of freezing. Insulate the outside cover.
But I've been told repeatedly that the dead men were smart and never did anything wrong, so, I guess it's A-OK. But if you do that today you're a dangerous hack.
When that home was build few power tools were used. Hand saw to cut and hammer to knock it out. Wasn't right then and still wrong.ChrisJ said:I would open that bay to the basement. Much less chance of freezing. Insulate the outside cover. Why do they notch floor Joyce like that? Consider sistering up or at least some plywood bolted and glued where those notches are.
My house, as well as many others I've been to have the joists notched around steam piping. But I've been told repeatedly that the dead men were smart and never did anything wrong, so, I guess it's A-OK. But if you do that today you're a dangerous hack.2 -
If you look close at the picture of the uninsulated pipe that's outside it almost looks like the pipe within the cavity is bent slightly. Also the riser isn't straight at a 90 and does kind of crook to the side. It definitely has pitch but maybe not enough. If it doesn't work after all this I may need to evaluate redoing that pipe. Just not sure if that thing will come off after being on for 90 years haha. Probably would need to cut the pipe and rethread after the T off the main. Again, all depends on if the insulation fixes the issue or not. If not then on to the next. If it's and issue with near boiler piping then it's a whole other thing. It never ends yet I genuinely enjoy working with this system.EBEBRATT-Ed said:To me the riser going up with no swing joint is a dead give away that the pipe is not pitched enough. In order to have the riser go up straight the pipe cannot be pitched.......or at least not pitched enough. You can't bend an elbow and "pipe sag" will not provide enough pipe pitch0 -
I have four long runouts and all of them have nothing more than a 90 on the end where it goes up to the 2nd floor from the basement. These are in the neighborhood of 10' long horizontally, 1 1/4" pipe.EBEBRATT-Ed said:To me the riser going up with no swing joint is a dead give away that the pipe is not pitched enough. In order to have the riser go up straight the pipe cannot be pitched.......or at least not pitched enough.
I can't say that it's right, but it does work on all of them.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
Cut the fitting, not the pipe, then you can screw a new fitting on the pipe.fxrgrunt said:If it doesn't work after all this I may need to evaluate redoing that pipe. Just not sure if that thing will come off after being on for 90 years haha. Probably would need to cut the pipe and rethread after the T off the main. Again, all depends on if the insulation fixes the issue or not. If not then on to the next. If it's and issue with near boiler piping then it's a whole other thing. It never ends yet I genuinely enjoy working with this system.
This looks like a good case for the blocks under the feet of the radiator.
Did you take apart the valve to make sure part of it didn't come loose and block the seat?0 -
@fxrgrunt
I would disconnect the union at the radiator and see if you can pull the riser up, if you could get it an inch or more it would probably help a lot. Maybe a little wood trimming would be needed.
If it comes up you can add a hanger or a shim to hold it up. Then you could put shims under the radiator (may be ugly) or shorten the riser to make it work.
Just bust off the CI elbow at the bottom of the riser and put a new elbow on with a new riser0 -
They're not.EBEBRATT-Ed said:@fxrgrunt
The near boiler piping looks ok if the sizes are right.
That boiler was made by Dunkirk, regardless of what brand name is on it, and these boilers are known for wet steam unless they are piped just so. The piping at the steam outlet is bushed down from 2-1/2" to 2", and the pipe supplying the main on the left is bushed down too. Can't tell with the other main.
Whoever installed that boiler did not read the instructions. Here's the diagram if you're only using one steam outlet:
Consulting1 -
And here's the diagram when using both outlets, which is essential on larger models in this series:
Consulting1 -
If you look at the OP's other posts, there are posts about surging and skimming which would seem to indicate the problem is wet steam.0
show the radiator also,
is it possible you have too fast of a vent on that rad, and you're pulling condensate up there ?
how is the main venting in the basement ?known to beat dead horses0 -
It is but I also only started messing with the boiler last year. Which was my first full winter in the home. I don't believe previous owners ever touched it or did anything from 2014 to 2019. It had tons of oils/contaminants in the boiler so I skimmed and cleaned. A lot was clogged up. I added too much treatment in and had to clear that out. I definitely am getting wet steam but I'm not sure if that is the particular cause for that radiator because of it being uninsulated. After this winter I will probably have the near boiler piping redone to take that equation out. Unfortunately there is noone on this forum close to the Albany New York area. Lots of guys about 2 hours away in Mass and NJ though. Maybe someone would be willing to travel.mattmia2 said:If you look at the OP's other posts, there are posts about surging and skimming which would seem to indicate the problem is wet steam.0 -
Radiator has a Hoffman 1A. I have had it all the way open and at lowest setting. On the 64ft main line I have a gorton 2 and hoffman 75 which I plan to Chang to two gorton 2s. I have 3 MOM vents on the shorter 45ft main. My plan is to take the hoffman 75 from the other main and just add as the 4th on my antler to the 3 MOMs. Picture of radiator attached.neilc said:show the radiator also, is it possible you have too fast of a vent on that rad, and your pulling condensate up there ? how is the main venting in the basement ?
others here will need to check me on this,
but I think the hoffman adjustables are still a fast vent, even when shut down,
and same others will suggest a different vent,known to beat dead horses0 -
Is that valve the same as other radiators? That looks like it might be a modulating valve used on 2 pipe systems but others will know better than me. I assume it is open fully, but I am still suspicious.0
There was like 3 or 4 of them which look to be original. They are gortons. I repacked them last year as well. Straight out they are open and turned to the left or right They are closed.mattmia2 said:Is that valve the same as other radiators? That looks like it might be a modulating valve used on 2 pipe systems but others will know better than me. I assume it is open fully, but I am still suspicious.0 -
Hoffman 1As are very difficult to adjust and have so much slop they can by wide open or fully closed at pretty much any number on the cap.
Completely remove the nut and the cap and see if it heatsSingle pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.