Un-Insulated Steam Pipe Issue
Comments
-
More pictures.0
-
That will help I am sure. Just make sure that everything is well pitched before you close it up.
I am suspicious of not having enough pitch on the runout to the radiator and my reason is that the riser going through the floor up to the radiator only has 1 elbow, no swing joint which tells me the horizontal pipe is basically flat. Check the pitch of the radiator also.
I would hate to see you close it up after all that work and not have it fixed.
1 -
Insulation is good. But I predict your problem will remain. I had 3 radiators supplied by 1” pipe in uninsulated exterior walls and they supplied fine.
I suspect you might have incorrect near boiler piping that is causing water to be thrown up into the main and to the kitchen radiator.NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
EBEBRATT-Ed said:That will help I am sure. Just make sure that everything is well pitched before you close it up. I am suspicious of not having enough pitch on the runout to the radiator and my reason is that the riser going through the floor up to the radiator only has 1 elbow, no swing joint which tells me the horizontal pipe is basically flat. Check the pitch of the radiator also. I would hate to see you close it up after all that work and not have it fixed.0
-
ethicalpaul said:Insulation is good. But I predict your problem will remain. I had 3 radiators supplied by 1” pipe in uninsulated exterior walls and they supplied fine.
I suspect you might have incorrect near boiler piping that is causing water to be thrown up into the main and to the kitchen radiator.0 -
I would open that bay to the basement. Much less chance of freezing. Insulate the outside cover.
Why do they notch floor Joyce like that? Consider sistering up or at least some plywood bolted and glued where those notches are.0 -
pecmsg said:I would open that bay to the basement. Much less chance of freezing. Insulate the outside cover. Why do they notch floor Joyce like that? Consider sistering up or at least some plywood bolted and glued where those notches are.0
-
My house, as well as many others I've been to have the joists notched around steam piping.pecmsg said:I would open that bay to the basement. Much less chance of freezing. Insulate the outside cover.
Why do they notch floor Joyce like that? Consider sistering up or at least some plywood bolted and glued where those notches are.
But I've been told repeatedly that the dead men were smart and never did anything wrong, so, I guess it's A-OK. But if you do that today you're a dangerous hack.
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
ChrisJ said:
I would open that bay to the basement. Much less chance of freezing. Insulate the outside cover. Why do they notch floor Joyce like that? Consider sistering up or at least some plywood bolted and glued where those notches are.
My house, as well as many others I've been to have the joists notched around steam piping. But I've been told repeatedly that the dead men were smart and never did anything wrong, so, I guess it's A-OK. But if you do that today you're a dangerous hack.2 -
-
EBEBRATT-Ed said:To me the riser going up with no swing joint is a dead give away that the pipe is not pitched enough. In order to have the riser go up straight the pipe cannot be pitched.......or at least not pitched enough. You can't bend an elbow and "pipe sag" will not provide enough pipe pitch0
-
I have four long runouts and all of them have nothing more than a 90 on the end where it goes up to the 2nd floor from the basement. These are in the neighborhood of 10' long horizontally, 1 1/4" pipe.EBEBRATT-Ed said:To me the riser going up with no swing joint is a dead give away that the pipe is not pitched enough. In order to have the riser go up straight the pipe cannot be pitched.......or at least not pitched enough.
You can't bend an elbow and "pipe sag" will not provide enough pipe pitch
I can't say that it's right, but it does work on all of them.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
Cut the fitting, not the pipe, then you can screw a new fitting on the pipe.fxrgrunt said:If it doesn't work after all this I may need to evaluate redoing that pipe. Just not sure if that thing will come off after being on for 90 years haha. Probably would need to cut the pipe and rethread after the T off the main. Again, all depends on if the insulation fixes the issue or not. If not then on to the next. If it's and issue with near boiler piping then it's a whole other thing. It never ends yet I genuinely enjoy working with this system.
0 -
0
-
This looks like a good case for the blocks under the feet of the radiator.
Did you take apart the valve to make sure part of it didn't come loose and block the seat?0 -
@fxrgrunt
I would disconnect the union at the radiator and see if you can pull the riser up, if you could get it an inch or more it would probably help a lot. Maybe a little wood trimming would be needed.
If it comes up you can add a hanger or a shim to hold it up. Then you could put shims under the radiator (may be ugly) or shorten the riser to make it work.
Just bust off the CI elbow at the bottom of the riser and put a new elbow on with a new riser0 -
They're not.EBEBRATT-Ed said:@fxrgrunt
The near boiler piping looks ok if the sizes are right.
That boiler was made by Dunkirk, regardless of what brand name is on it, and these boilers are known for wet steam unless they are piped just so. The piping at the steam outlet is bushed down from 2-1/2" to 2", and the pipe supplying the main on the left is bushed down too. Can't tell with the other main.
Whoever installed that boiler did not read the instructions. Here's the diagram if you're only using one steam outlet:
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
And here's the diagram when using both outlets, which is essential on larger models in this series:
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
If you look at the OP's other posts, there are posts about surging and skimming which would seem to indicate the problem is wet steam.0
-
show the radiator also,
is it possible you have too fast of a vent on that rad, and you're pulling condensate up there ?
how is the main venting in the basement ?known to beat dead horses0 -
mattmia2 said:If you look at the OP's other posts, there are posts about surging and skimming which would seem to indicate the problem is wet steam.0
-
neilc said:show the radiator also, is it possible you have too fast of a vent on that rad, and your pulling condensate up there ? how is the main venting in the basement ?0
-
others here will need to check me on this,
but I think the hoffman adjustables are still a fast vent, even when shut down,
and same others will suggest a different vent,known to beat dead horses0 -
Is that valve the same as other radiators? That looks like it might be a modulating valve used on 2 pipe systems but others will know better than me. I assume it is open fully, but I am still suspicious.0
-
mattmia2 said:Is that valve the same as other radiators? That looks like it might be a modulating valve used on 2 pipe systems but others will know better than me. I assume it is open fully, but I am still suspicious.0
-
0
-
Hoffman 1As are very difficult to adjust and have so much slop they can by wide open or fully closed at pretty much any number on the cap.
Completely remove the nut and the cap and see if it heatsSingle pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements