Chimney-As-Chase

JohnNY
JohnNY Member Posts: 3,324
Hello all,
I'm having trouble finding a National Fuel Gas Code for repurposing a masonry chimney to be used as a chase containing not only (either) CPVC/Polypropylene/AL29-4C boiler venting to the roof but also a gas line to a rooftop generator and an electrical conduit to the same generator all in the same chase. This can't be an approved installation but I can't illustrate it to the building. Any guidance to a defining Code is appreciated.
Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 18,035
    What if it was a wooden chase boxed in by sheetrock? That would pass. Just because it used to be a chimney I don't see a problem.

    Is this existing or a proposed retrofit?
  • pecmsg
    pecmsg Member Posts: 6,216
    My only concern is the Fuel Piping! It "May" have to be double piped and vented.
  • Zman
    Zman Member Posts: 7,611
    Is this a commercial building?
    I think chapter 7 of the IBC addresses it.
    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein
  • JohnNY
    JohnNY Member Posts: 3,324
    Zman said:

    Is this a commercial building?
    I think chapter 7 of the IBC addresses it.

    Yes it is.