Ignitor OHMs
Shouty
Shouty Member Posts: 2
Does anyone have a chart with the range of OHMs for ignitors? Can't seem to find anything on Google.
  • Ironman
    Ironman Member Posts: 7,934
    What type of igniter are you referring to?
    Since the electrode is solid metal, I would expect there would be no resistance.
    Bob Boan
  • Ironman
    Or are you referring to a hot surface igniter?
    Bob Boan
  • Shouty
    Hot surface ignitor. Sorry, I should have been more specific.
  • Ironman
    I’ve never tried to ohm out one, nor heard of that approach. If it heats up and has no visible cracks or defects, then I’d assume it’s good.
    Some older furnaces also used it as the flame sensor and had issues doing that. They switch to using a flame rod and made a retrofit kit for that.
    Bob Boan
  • Tim McElwain
    Tim McElwain Member Posts: 4,660
    The Room Temperature Resistance (RTR) for a Model 201 is 45 to 400 ohms, the 271 is 45 to 75 ohms those are Silicon Carbide Igniters. The Silicon Nitride Igniters are less resistance around 8 to 20 ohms.
    mattmia2 Member Posts: 17,591
    HSI ignitors act as PTC termistors so the cold resistance is much lower than the power rating and ohm's law would predict.