Ignitor OHMs
Does anyone have a chart with the range of OHMs for ignitors? Can't seem to find anything on Google.
  • Ironman
    Ironman Posts: 7,967
    What type of igniter are you referring to?
    Since the electrode is solid metal, I would expect there would be no resistance.
    Bob Boan
  • Ironman
    Or are you referring to a hot surface igniter?
    Bob Boan
  • Hot surface ignitor. Sorry, I should have been more specific.
  • Ironman
    I’ve never tried to ohm out one, nor heard of that approach. If it heats up and has no visible cracks or defects, then I’d assume it’s good.
    Some older furnaces also used it as the flame sensor and had issues doing that. They switch to using a flame rod and made a retrofit kit for that.
    Bob Boan
  • The Room Temperature Resistance (RTR) for a Model 201 is 45 to 400 ohms, the 271 is 45 to 75 ohms those are Silicon Carbide Igniters. The Silicon Nitride Igniters are less resistance around 8 to 20 ohms.
    mattmia2 Posts: 18,254
    HSI ignitors act as PTC termistors so the cold resistance is much lower than the power rating and ohm's law would predict.