Running MOD-CON boiler for Radiant Heat on generator during power outage-Any Suggestion?

Options
hcpatel78
hcpatel78 Member Posts: 154
edited August 2021 in Radiant Heating
Hi All,
I am just exploring the back up generator for my house. I also have radiant heat with Mod-Con boiler install which uses Natural Gas as a fuel. Do anyone have experience with the generator using to run this kind of the deliciated full of electronics combi boilers without damaging any electronics?
I was just reading that most of the generator is not supplying clean power (mean has Total harmonic distortion is around 11 to 15%) except those expensive inverter generator so...
I have Noritz CB199 model of Mod-Con and Grundfos Alpha II circulator in Radiant heat system.
Any advice...?
Thank you,
hiren
Thank you,
Hiren Patel

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 26,125
    If you want to be safe -- particularly with a less expensive generator -- your best bet is to run the boiler through and UPS. Two advantages -- first, it will clean up the power. Second, it will carry the boiler for a while while you get the generator running. But get a good one, which produces sine wave power. They aren't all that cheap either, of course, but APC makes some good ones.

    You may also be able to find some older -- like, very older -- brush excited generators which have pretty clean power.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    mattmia2
  • mattmia2
    mattmia2 Member Posts: 13,276
    If it were me i'll roll the dice, but I would look for a used full time online UPS that just needs new batteries.
  • Jamie Hall
    Jamie Hall Member Posts: 26,125
    mattmia2 said:

    If it were me i'll roll the dice, but I would look for a used full time online UPS that just needs new batteries.

    That would work, if it worked at all!
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    I have a whole house Koehler. Works fine. Dont go cheap.

    There was an error rendering this rich post.

  • Derheatmeister
    Derheatmeister Member Posts: 1,658
    We installed a Viessmann WB2A 11/44 about 15 years ago in Camp Hale Colorado..
    This Off grid system is powered via a PV system with a backup Kohler generator switched via Outback..Back then Viessmann did not approve of this installation.
    To protect the boilers Electronics and give the boiler a good sine wave we installed a APC UPS and never had any issues.
    Zman
  • hcpatel78
    hcpatel78 Member Posts: 154
    edited August 2021
    Great suggestions. Thank you all.