Corrosion in nearly new steam boiler
Where is the corrosion and can you post some pictures?? We would like to see it. Lots of variables.
A seven year old boiler should not fail unless using excessive make up water0 -
Is the boiler using softened water? Depending on the softener, that can kill a boiler in remarkably quick time. Or, as @EBEBRATT-Ed said, leaks. Or both...Br. Jamie, osb
What model Burnham?All Steamed Up, Inc.
Consulting0 -
I can't quite understand exactly if you're using soft water or not in your boiler, but not draining it every year is fine IMO (I like to drain as little as possible to let the mud out).
I'm really sorry about your boiler. Try a Peerless
Here is everyone's recent opinions on oil vs gas when you have the option: https://forum.heatinghelp.com/discussion/184685/convert-to-gas-or-stay-with-oilNJ Steam Homeowner.
the boiler unit is Burnham M/N KV89 (KV89LX-LLUDO, S/N G5026585) I am attaching photos of the burner and corrosion and I will post pics of water softener and front view of unit and the burner looping
more pics on other components and views0
Yes I am using the softened water in both the boiler and my oil fired hot water heater. Thankful they are separate because I do have hot water0
My eyes are not the best but I am not seeing corrosion.0
That's a lot of your problem in the boiler. Do NOT use softened water in a boiler. For a hot water system, if your source water is really hard, use deionized or distilled water and chemical pH and oxidation treatment. For steam, simple pH stabilization is all that's needed for residential use. Softened water is remarkably corrosive.nysger said:Yes I am using the softened water in both the boiler and my oil fired hot water heater. Thankful they are separate because I do have hot water
Bad move. Softened water contains sodium chloride (salt) ions, which accelerate corrosion in cast-iron boilers.nysger said:Yes I am using the softened water in both the boiler and my oil fired hot water heater. Thankful they are separate because I do have hot water
Based on the rating of that boiler, you're really into a small commercial boiler size. Look at the Weil-McLain 80 series, Peerless SC or similar. These can all burn oil or gas.
Where are you located?All Steamed Up, Inc.
Consulting0 -
Maybe measure the EDR first and make sure the current boiler isn't grossly oversized...Steamhead said:
Where are you located?2 -
I live in Poughkeepsie my 12603. Can someone explain EDR for me. Thanks.
Also if I change my boiler to gas can my hot water heater stay oil fired and share the same chimney…a stainless steel liner insert exists in the chimney.0 -
EDR= Equivalent Direct Radiation. Basically, how much heat your radiators can emit.All Steamed Up, Inc.
Consulting0 -
No. At least around here gas and oil cannot share a chimney.nysger said:I live in Poughkeepsie my 12603. Can someone explain EDR for me. Thanks.
Also if I change my boiler to gas can my hot water heater stay oil fired and share the same chimney…a stainless steel liner insert exists in the chimney.Br. Jamie, osb
Would a PH neutralizer system work in my case? To neutralize my acidic water.0
You may want a pH neutralizer for all of your water, if it is really acidic However... most residential pH neutralizes also increase the hardness; you mentioned that you had a water softener now, so I'm guessing that your water is also somewhat hard already. This is a somewhat unusual pairing -- usually hard water is pretty close to neutral pH, and acidic water not particularly hard, but...
For you boiler, the best treatment is probably Rectorseal or something of the sort, just enough to get the pH up to 8 or so. If you don't use much or any water, that will be just fine. No softening! For your domestic water, you may want to balance the control of pH -- if the water is really acidic, say around 4 or so, that can be hard on copper plumbing -- with desired softness. I personally would be more concerned about the acidity of domestic water than about hardness, but there is an aesthetic part to that equation.Br. Jamie, osb
I live and work in the same area. Definitely cannot vent both into the same chimney. An inspector will definitely catch that in Poughkeepsie. I would go with gas heating over oil if you do end up replacing anything. I would change the water heater too and just be done with the oil, as much as I like oil equipment natural gas is less expensive in Dutchess County. Be very careful with who you hire to do the work. I don't know anyone in the area who I would consider a competent steam company, I don't work on any myself. That boiler seems ridiculously large for a home in the town of Poughkeepsie, I would definitely recommend figuring out how much radiation your emitters are capable of, that is the EDR and determines the size of the boiler for your home. I wouldn't be surprised if it is massively oversized knowing some of the companies in our area. I didn't see major corrosion either in your pictures but hearing about the softened water and that fact that you have a Burnham I wouldn't be surprised if you have a problem. I would also recommend a Peerless boiler if you end up replacing everything.Jamie Hall said:I live in Poughkeepsie my 12603. Can someone explain EDR for me. Thanks. Also if I change my boiler to gas can my hot water heater stay oil fired and share the same chimney…a stainless steel liner insert exists in the chimney.
No. At least around here gas and oil cannot share a chimney.2 -
As far as I know, gas and oil is allowed in CT. The question comes up often, but have yet to find the code for it. Do you have a code number?0
Ok so softened water is not good for cast iron boilers…point well made. So is there something to take the hardness out of my well water yet not introduce acidity to my water and that I can use for the whole house?0
A little confusion there, I think. Acidity -- pH -- refers to the concentration of the Hydrogen H+ ion in the water. Hardness refers to the combined concentration of Calcium CA+2 and Magnesium MG+2 ions (usually almost entirely Calcium). They do have an effect on each other; in general, hard water -- high Calcium concentration -- will have a moderate to high pH, whereas naturally soft water will tend to have a lower pH.
Most residential water softeners work by exchanging Sodium ions, Na+, for Calcium ions. Two things happen (I'll not get into the equilibrium chemistry involved): first, water with a significant Sodium ion concentration tends to be highly corrosive. Think salt water -- sea water. Second, at the same time, removing the Ca+ ions reduces what is called the buffering capacity of the water -- a property of the various compounds dissolved in the water which stabilises the pH -- and, as a result, will reduce the pH of the water -- make it more acid.
Bottom line. Most domestic water softeners remove Calcium ions and add Sodium ions and lower -- make more acid -- the pH. Most domestic devices to control acidity -- raise the pH -- do so by adding Calcium ions to raise and stabilise the pH.
In principle it is possible to reduce the Calcium concentration -- the hardness -- and control the acidity -- stabilise the pH (the usual target value is around 7.5) with water treatment. So far as I am aware, there is no combination of common domestic water treatment devices which will do that. It is done in large water treatment facilities -- under the constant watch and control of the plant operators -- by adding various chemicals to the water in precise amounts and then settling and clarifying the water.
In your situation, I would plan on using the well water as is -- possibly with Rectorseal or some such to stabilise the pH -- and adding a water softener for the domestic water supply only -- probably only on the hot water.Br. Jamie, osb
Jamie hall thanks for the analysis. Your solution makes a lot of sense and I will try to implement.0
