Will a Hole in the Flue Pipe cause pressure switch to stick open?
Dairon421
Member Posts: 81
Hey guys so I'm working on a Locknivar boiler Cwn0645pm(model). The inducer and hoses are fine and I replaced the pressure switch and still no action. So I inspected the venting and saw a big gap. Don't have the materials to fix it but will that be a reason why the switch not working completing the circuit?
(Also I'm not getting correct W.C to switch)
(Also I'm not getting correct W.C to switch)0
I don't believe the pressure switch would be affected by that opening. I do believe that opening could allow carbon monoxide to enter the living space.
Don't operate that boiler until you get the vent repaired.
Mr.Ed
PS. Your annual maintenance and inspection service should have identified that 2 years ago. That did not happen in the last few months.Edward Young Retired
I assumed you are the business or homeowner because as a professional, you would not attempt to repair the pressure switch with a defective venting system. You would know better.
damn
thats not a hole.That’s a canyon.Shut it down0 -
duct tape0
I agree with "not safe to run"
Is this a fan assisted flue?0 -
Judging by the corrosion on the flue pipe, I'd be looking for a hole in the HX that's keeping the pressure switch from making.
It's likely quite dangerous, a 'kill the whole family' kind of thing. Shut it down until it can be thoroughly checked.
- 167 Indoor-Air Quality
