line set leak at contact with mineral wool insulation
Options
scottx
Posts: 2
Where there was direct contact with the line set by mineral wool blown-in insulation we had had two leaks. Nowhere else in the 30 foot run that has the foam factory insulation has had an issue. This is a 2 foot foot long section and has leaked 2 times prior.
Is there an issue with cold moist copper and contact with mineral wool? thanks....
Is there an issue with cold moist copper and contact with mineral wool? thanks....
0
Comments
-
The ultimate issue is that the copper is paper thin so the tiniest defect causes a leak, but the mineral wool might be slightly acidic.0
-
Just did a little more digging. Mineral wool has a high Ph. Too acid or alkaline seems to be a problem with copper, probably other metals too.0
-
Combination of the mineral wool and it's holding moisture next to the copper. The lineset should be sleeved through there.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Why was the suction line N O T insulated with the insulation ends sealed?0