line set leak at contact with mineral wool insulation
Where there was direct contact with the line set by mineral wool blown-in insulation we had had two leaks. Nowhere else in the 30 foot run that has the foam factory insulation has had an issue. This is a 2 foot foot long section and has leaked 2 times prior.
Is there an issue with cold moist copper and contact with mineral wool? thanks....
    mattmia2 Posts: 18,236
    The ultimate issue is that the copper is paper thin so the tiniest defect causes a leak, but the mineral wool might be slightly acidic.
  • scottx
    scottx Posts: 2
    Just did a little more digging. Mineral wool has a high Ph. Too acid or alkaline seems to be a problem with copper, probably other metals too.
    Jamie Hall Posts: 27,909
    Combination of the mineral wool and it's holding moisture next to the copper. The lineset should be sleeved through there.
    pecmsg Posts: 7,613
    Why was the suction line N O T insulated with the insulation ends sealed?
