new boiler circulation issue
nytech28
Member Posts: 116
in Gas Heating
hello I had a visit on a brand new boiler that was relocated to another location from the original place , has two circulation pumps for the 1st & 2nd flr , but no hot water circulation to either floors baseboards, after confirming theres no issue with pumps ,I tryed bleeding air at the boiler ,but am not getting any water returning back to boiler from either zones when I open hose bibs on the return piping , the owner temporary has electric heaters installed to warm house.any recommendations would help to solve this issue,plz see pictures of the piping & boiler ,plz update
Funny , I see a BFP but no PRV ?
I would try purging system with a pool pump purge set up. Pex has high head loss, and has many high and low spots due to sag. Are those taco 005 circulators? Maybe circulators cannot push the air out of all unvented high spots in pex?0
Don't take the wrong way but....
You are attracting the wrong kind of customer. Both this one and your previous post were installed by totally incompetent people. https://forum.heatinghelp.com/discussion/181049/zone-pipe-work#latest
I would recommend walking away from this unless the are willing to pay you to make this right.
Albert Einstein10 -
Have you (can you) bleed at the radiators instead of at the boiler?
Amateur question here, but isn't that unsupported expansion tank and circulator arrangement putting a ridiculous load on the boiler casting?0 -
What is that green wire doing? Or is it tubing?
You will have to add some valves to purge properly.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
update on boiler issue from march 6 post, I installed air vents on baseboards for both zones & was able to vent out all air ,also I installed taco 0011 pump to get better circulation for the 1st flr,originall taco pump was 007 .I would say I dont like the way the system was piped to many fittings no pipe support ,also spoke with manufacturer they recommend the supply & return being on the same side of the boiler ,being 20° outside ,I had to work with what was already there. Final result am getting good heat & a happy customer. I appreciate everyone responding to my post.I tryed explaining it in simple terms ,hope this helps me & you guys as well.thanks
2 -
it's my pipe clamp thermometer to check return water tempWhat is that green wire doing? Or is it tubing? You will have to add some valves to purge properly.
yes to many things not rite I got them heat in the cold weather, but needs further work.MaxMercy said:Have you (can you) bleed at the radiators instead of at the boiler? Amateur question here, but isn't that unsupported expansion tank and circulator arrangement putting a ridiculous load on the boiler casting?1 -
I do remember the previous post, I do have an updated pipe arrangement that will be installed on the new boiler once the homeowner is ready to install new boiler.thanksZman said:Don't take the wrong way but.... You are attracting the wrong kind of customer. Both this one and your previous post were installed by totally incompetent people. https://forum.heatinghelp.com/discussion/181049/zone-pipe-work#latest I would recommend walking away from this unless the are willing to pay you to make this right.1 -
taco 007 upgreded.to taco 0011 ,made big difference.chuckadoo said:I would try purging system with a pool pump purge set up. Pex has high head loss, and has many high and low spots due to sag. Are those taco 005 circulators? Maybe circulators cannot push the air out of all unvented high spots in pex?1 -
And the vent opening is properly capped to prevent the water from leaking out too. NOTBig Ed_4 said:Funny , I see a BFP but no PRV ?
1
- 119 Chimneys & Flues
- 76 Pipe Deterioration