Near Boiler Plumbing Help (Burnham PIN7SNI-ME2)
I don't know the exact model, but that looks just like mine. Mine also only has one riser used. My understanding is that that is less important than the rest of the near boiler piping, which others here will weigh in on no doubt. at any rate I can see that the near boiler piping is more correct than mine.
Mine works fine with the single riser. I've read that while both riser ports can be used, an advantage of there being two spots available (even if only one is used) on top is that it makes it easier on teh installer by allowing an extra option to avoid obstructions.New owner of a 1920s home with steam heat north of Boston.
Just trying to learn what I can do myself and what I just shouldn't touch1 -
It depends on the size of the boiler and it's indicated in the installation manual, which you should have a copy of near the boiler (the installer should leave it there because the inspector needs it to be there)
According to the manual from Burnham the IN7 is supposed to use both risers. So they piped it wrong.3
Au contraire, @bucksnort - the "book" is what the manufacturer says is proper for that unit, so with only one riser that installation is wrong. Not only that, but the horizontal portion of the header needs to be 3-inch, and the installer only used 2-inch, so that's wrong too.
The manual is here: https://app.catsy.com/app/share/782/o/lightboxes/4067983986
You'll note that the riser from the header is 2-inch but then connects to a 2-1/2" or 3" steam main with a reducing coupling. That alone would indicate the near-boiler piping is wrong. There is enough radiation on this system that the larger piping is needed.
@mjc4370 , they need to re-pipe this. The improper piping will reduce your efficiency and may cause banging.All Steamed Up, Inc.
Consulting3 -
The manual wants both risers used, when are "WE" allowed to rewrite the manual?bucksnort said:Are you having problems with heat? If not why are we worried because a book says it should? A book doesn't cover every situation. Now if there is a heat problem the installer will be on the hook to explain why it's not working.
If this was inspected (Code being a bear bones minimum standard) it wouldn't pass due to 1 riser.1 -
How about a skim port? There is a plug somewhere for that, something you want removed and a nipple with at least a cap installed, before it get steam welded into place.
How about the existing bull head tee on what looks to be 2 separate mains?
No mention of this in the book, but I would guess many pros here would perhaps have 2 steam main risers.
Cleaning instructions are also included in the book as part of the installation.
Did the contractor do an EDR count of your radiators? You could be oversized (common occurrence) which will drop your efficiency even more.1 -
There is a skim port on the right side of the boiler near my indirect water heater. The company did come out and measure all of the radiators and sized this based on those measurements. I have a 3300 sq ft. home and it has 14 radiators. I don’t seem to be having issues currently but I also wouldn’t know if its less efficient than it should be. I guess my real concern is that since I paid almost $ for the conversion I want it done right and I do not want the warranty to be voided because it’s not installed correctly.0
@mjc4370
This is easy. They didn't follow the manufacturers MINIMUM piping requirements. Will it work? Maybe. But you may pay in problems down the road and in higher fuel bills.
Look at the water level while it is steaming. Is it steady? A little bouncing is ok
Find the boiler manual or download it if it's not there. There will be a piping diagram for your model boiler.
As far as pipe sizes go just so you can check what you have
1 1/2" pipe is about 2" OD
2" pipe is 2 3/8 OD
2 1/2" is about 3"
and 3" pipe is 3 1/2 OD
Too bad because it looks like they did a nice job other than undersizing the pipe0 -
Good call. I missed that they had down sized piping.Steamhead said:Au contraire, @bucksnort - the "book" is what the manufacturer says is proper for that unit, so with only one riser that installation is wrong. Not only that, but the horizontal portion of the header needs to be 3-inch, and the installer only used 2-inch, so that's wrong too.
As for install instructions, if the owner ever had a warranty claim and a boiler rep came out the owner would be SOL.0