Traps
What happens when you replace a trap set at 15 with one set at 125. Will it still work, if not how would you know the 15 trap is the right one?
    Jamie Hall Member Posts: 27,214
    Say again? What kind of trap, and to what does "set at 15" refer?
  • Shane_2
    Shane_2 Member Posts: 200
    If by some chance you a talking about replacing a 15lb pressure relief valve with a 125lb pressure relief valve on a steam boiler, NO----DO NOT DO THAT!! That is a safety device and needs to be replaced with the same
    Steamhead Member Posts: 18,393
    @Redyed , what is this trap connected to?
    In general, a trap rated for higher pressure has a smaller valve orifice, so it won't do a good job of passing condensate or air at lower pressures.
    Consulting
    EBEBRATT-Ed Member Posts: 20,063
    @Redyed
    What @Steamhead said.
    Two traps the same pipe size 1 rated at 15 the other rated at 125 the 125 will have a smaller orifice. It will "work" but may not have the capacity you need