What happens when you replace a trap set at 15 with one set at 125. Will it still work, if not how would you know the 15 trap is the right one?

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 15,350
    Say again? What kind of trap, and to what does "set at 15" refer?
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.
    Hoffman Equipped System (all original except boiler), Weil-Mclain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch
  • Shane_2
    Shane_2 Member Posts: 138
    If by some chance you a talking about replacing a 15lb pressure relief valve with a 125lb pressure relief valve on a steam boiler, NO----DO NOT DO THAT!! That is a safety device and needs to be replaced with the same
  • Steamhead
    Steamhead Member Posts: 14,326
    @Redyed , what is this trap connected to?

    In general, a trap rated for higher pressure has a smaller valve orifice, so it won't do a good job of passing condensate or air at lower pressures.
    All Steamed Up, Inc.
    "Reducing our country's energy consumption, one system at a time"
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Baltimore, MD (USA) and consulting anywhere.
    https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 8,519
    @Redyed

    What @Steamhead said.

    Two traps the same pipe size 1 rated at 15 the other rated at 125 the 125 will have a smaller orifice. It will "work" but may not have the capacity you need