Traps
Redyed
Member Posts: 1
What happens when you replace a trap set at 15 with one set at 125. Will it still work, if not how would you know the 15 trap is the right one?
Say again? What kind of trap, and to what does "set at 15" refer?Br. Jamie, osb
If by some chance you a talking about replacing a 15lb pressure relief valve with a 125lb pressure relief valve on a steam boiler, NO----DO NOT DO THAT!! That is a safety device and needs to be replaced with the same0
@Redyed , what is this trap connected to?
In general, a trap rated for higher pressure has a smaller valve orifice, so it won't do a good job of passing condensate or air at lower pressures.All Steamed Up, Inc.
Consulting0 -
@Redyed
What @Steamhead said.
Two traps the same pipe size 1 rated at 15 the other rated at 125 the 125 will have a smaller orifice. It will "work" but may not have the capacity you need0