Small baseboard heater no heat
Ianlovestish_05
Member Posts: 11
I have a new install boiler weil mclain cga-4 with taco 007e pump on single loop 1” with 3/4” baseboards. The bathroom baseboard won’t heat up I have purged it several times at the baseboard plenty of pressure and no air coming out. I’m stumped I can provide pictures any help appreciated
How is it piped? Monoflo loop?Bob Boan
Are your other baseboards heating? If it is a series loop they will all heat or not heat. If it's a monoflo loop it's a different story0
I’m pretty sure it’s mono flow it has a 1” loop with 3/8” branches off of it all other baseboards work fine0
The classic air bubble, look for a pipe pitched the wrong way. Worse case you’ll need to cut in a purge0
It's definitely an air pocket. If you have a coin vent on the baseboard you can easily get the air out.
I've heard a few drops of dawn dish detergent added to the boiler will help with air removal.0 -
I’ll try bleeding it again I have left it flow out at least 2 min before hope the installer put the correct mono flow t on there0
The perimeter loop and Tee's were replaced?
It wasn't just a boiler replacement? Sure, piping at the boiler was replaced but the branches were altered too?
They didn't reverse flow did they?
You might need to bleed that rad a lot longer than 2 minutes. It might take an hour. The long runs can be a real pain in the butt.0 -
The branches look original too me but there is some new copper piping where I believe they added the kitchen and bathroom ones the bathroom one is on the end of the loop I’ll try blending it longer0
Super, if the runout(s) or the bleeder is pitched incorrectly, you can bleed till you’re red in the face- ain’t gonna happen. Sometimes one can get lucky by man handling the upside down piping and get the bubble to move1
I’m back again I got the baseboard to get hot but it did not last I can hear air in the lines I don’t have a purge station just a drain I’ll post pics this time
As pics show there is no purge station and I can get the bathroom baseboard hot buy putting a hose one the drain and opening the fill valve but it won’t last0
Any pictures of the old boiler and piping at it?0
That gas flex line is not allowed to enter the cabinet like that.Ianlovestish_05 said:
Read Dans book Pumping Away0 -
Hmm it passed city inspection with that gas line if it’s not code I’ll change it0
The old plumbing it where it branches off the loop is new this is what the home inspection came with0
Wow- code official passed that- wow0
Yes the did pass I was there with them I’ll change it immediately0
This is the baseboard I’m having trouble with it gurgles when its working and when it goes silent it stops
Code is Minimum, im surprised he didn't see that or maybe not!Ianlovestish_05 said:Yes the did pass I was there with them I’ll change it immediately
- 119 Chimneys & Flues
- 165 Indoor-Air Quality
- 76 Pipe Deterioration
- 15.6K Strictly Steam