Small baseboard heater no heat

I have a new install boiler weil mclain cga-4 with taco 007e pump on single loop 1” with 3/4” baseboards. The bathroom baseboard won’t heat up I have purged it several times at the baseboard plenty of pressure and no air coming out. I’m stumped I can provide pictures any help appreciated

Comments

  • Ironman
    Ironman Member Posts: 7,550
    How is it piped? Monoflo loop?
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,479
    Are your other baseboards heating? If it is a series loop they will all heat or not heat. If it's a monoflo loop it's a different story
  • Ianlovestish_05
    Ianlovestish_05 Member Posts: 11
    I’m pretty sure it’s mono flow it has a 1” loop with 3/8” branches off of it all other baseboards work fine
  • GW
    GW Member Posts: 4,832
    The classic air bubble, look for a pipe pitched the wrong way. Worse case you’ll need to cut in a purge
    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
  • SuperTech
    SuperTech Member Posts: 2,430
    It's definitely an air pocket. If you have a coin vent on the baseboard you can easily get the air out.
    I've heard a few drops of dawn dish detergent added to the boiler will help with air removal.
  • Ianlovestish_05
    Ianlovestish_05 Member Posts: 11
    I’ll try bleeding it again I have left it flow out at least 2 min before hope the installer put the correct mono flow t on there
  • HVACNUT
    HVACNUT Member Posts: 6,332
    > @Ianlovestish_05 said:
    > I’ll try bleeding it again I have left it flow out at least 2 min before hope the installer put the correct mono flow t on there


    The perimeter loop and Tee's were replaced?

    It wasn't just a boiler replacement? Sure, piping at the boiler was replaced but the branches were altered too?

    They didn't reverse flow did they?

    You might need to bleed that rad a lot longer than 2 minutes. It might take an hour. The long runs can be a real pain in the butt.
  • Ianlovestish_05
    Ianlovestish_05 Member Posts: 11
    The branches look original too me but there is some new copper piping where I believe they added the kitchen and bathroom ones the bathroom one is on the end of the loop I’ll try blending it longer
  • Ironman
    Ironman Member Posts: 7,550
    How about some pics of the piping, including the Tees for that branch?
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    SuperTech
  • GW
    GW Member Posts: 4,832
    Super, if the runout(s) or the bleeder is pitched incorrectly, you can bleed till you’re red in the face- ain’t gonna happen. Sometimes one can get lucky by man handling the upside down piping and get the bubble to move
    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
    SuperTech
  • Ianlovestish_05
    Ianlovestish_05 Member Posts: 11
    I’m back again I got the baseboard to get hot but it did not last I can hear air in the lines I don’t have a purge station just a drain I’ll post pics this time
  • Ianlovestish_05
    Ianlovestish_05 Member Posts: 11



  • Ianlovestish_05
    Ianlovestish_05 Member Posts: 11
    As pics show there is no purge station and I can get the bathroom baseboard hot buy putting a hose one the drain and opening the fill valve but it won’t last
  • JUGHNE
    JUGHNE Member Posts: 11,276
    Any pictures of the old boiler and piping at it?
  • pecmsg
    pecmsg Member Posts: 5,294




    That gas flex line is not allowed to enter the cabinet like that.
    Read Dans book Pumping Away
  • Ianlovestish_05
    Ianlovestish_05 Member Posts: 11
    Hmm it passed city inspection with that gas line if it’s not code I’ll change it
  • Ianlovestish_05
    Ianlovestish_05 Member Posts: 11
    edited January 2021
    The old plumbing it where it branches off the loop is new this is what the home inspection came with
  • GW
    GW Member Posts: 4,832
    Wow- code official passed that- wow 
    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
  • Ianlovestish_05
    Ianlovestish_05 Member Posts: 11
    Yes the did pass I was there with them I’ll change it immediately
  • Ianlovestish_05
    Ianlovestish_05 Member Posts: 11
    This is the baseboard I’m having trouble with it gurgles when its working and when it goes silent it stops

  • pecmsg
    pecmsg Member Posts: 5,294

    Yes the did pass I was there with them I’ll change it immediately

    Code is Minimum, im surprised he didn't see that or maybe not!