Wet return
 
            
                
                    347                
                
                    Member Posts: 149                
            
                        
            
                    Hello all,
Has anyone used megapress on a wet return? I need to replace a small section and was thinking it might be wui
                Has anyone used megapress on a wet return? I need to replace a small section and was thinking it might be wui
0                
            Comments
- 
            Sorry about the cut off.
 Thinking it might be quicker then screw pipe. Pros, cons?
 Thanks0
- 
            I believe the o-ring in the fitting is rated for a high enough temperature to use on a wet return. It might even work on dry returned. There was a discussion on this topic before relating to using press fittings on mains and risers. The jury is still out on that question. manufacturer literature says OK but very little experience in the field on the swing joint function with temperature change/expansion and the like.Edward Young Retired After you make that expensive repair and you still have the same problem, What will you check next? 0
- 
            From what the Veiga rep has told me and in there literature that megapress is rated for low pressure steam.0
- 
            Wet returns you should have no problem with megapress. Temperatures are quite low -- or should be!Br. Jamie, osb
 Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
- 
            Thank you al for your replies. I'm doing the job tomorrow and I'll let you know how it went.0
- 
            MEGA Press is rated for low pressure steam so using it for wet returns is fine............Unless the old pipe that you connect to is pitted0
- 
            The pro press went really well.
 Take a look at the boiler header, see anything wrong?    
 0
- 
            
- 
            
- 
            Looking at that boilers piping leads to one thing and that is the installer is clueless you need to find a new installer . That is not even close to being correct and it must be under performing . Contact and pro and get it piped correctly, this would be the right thing to do and as many have stated steam system will usually work no matter how badly piped they are the difference is when working correctly there simple and work properly and like all properly designed heating system u would never know it on because your comfortable and don’t need to know if it is on or not that’s what it’s all about comfort . Peace and good luck clammyR.A. Calmbacher L.L.C. HVAC 
 NJ Master HVAC Lic.
 Mahwah, NJ
 Specializing in steam and hydronic heating1
Categories
- All Categories
- 87.2K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 427 Carbon Monoxide Awareness
- 118 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 112 Geothermal
- 164 Indoor-Air Quality
- 3.7K Oil Heating
- 73 Pipe Deterioration
- 1K Plumbing
- 6.4K Radiant Heating
- 393 Solar
- 15.5K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements