Banging radiator after relocation

This discussion was created from comments split from: Steam heating issues.
0
Leave a Comment
Categories
- 80.9K THE MAIN WALL
- 2.5K A-C, Heat Pumps & Refrigeration
- 36 Biomass
- 394 Carbon Monoxide Awareness
- 2.6K Controls
- 1.4K Domestic Hot Water
- 3.7K Gas Heating
- 100 Geothermal
- 130 Indoor-Air Quality
- 2.3K Oil Heating
- 30 Pipe Deterioration
- 560 Plumbing
- 4.2K Radiant Heating
- 333 Solar
- 12.1K Strictly Steam
- 36 Water Quality
- 7 Industry Classes
- 52 Job Opportunities
- 7 Recall Announcements
Comments
Chances are your problem is that the pipe was, indeed, laid down incorrectly, without adequate pitch. The only solution is going to be to change things so that it has adequate pitch... a smaller radiator might lessen the problem, but not eliminate it -- and would be addressing the symptom, not the problem!
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.
Hoffman Equipped System (all original except boiler), Weil-Mclain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.
Hoffman Equipped System (all original except boiler), Weil-Mclain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.
Hoffman Equipped System (all original except boiler), Weil-Mclain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch
steam will stop the flow of the condensate and banging will occur
Two corrections are possible.
1. try to get at least 4" of pitch on the horizontal supply to the radiator.
2. Increase the size of the horizontal pipe one size. That would entail replacing the the riser elbow one size (example 1 1/4" X 1 1/2" elbow with a piece of 1 1/2" pipe and at the radiator supply reduce from 1/1/2" pipe with a 1 1/2" x 1 1/4 Elbow to supply the radiator and Pitch the pipe with at least 1/2" of pitch ).
Jake
by Jacob (Jake) Myron
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.
Hoffman Equipped System (all original except boiler), Weil-Mclain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch