A clever Calefactio pump iso valve, check ∆P
hot_rod
Member Posts: 27,384
1/8" gauge ports, rotating flanges, and you can purge from either side, depending on handle position.
neat gadget!Br. Jamie, osb
Who's got 'em?Bob Boan
Would you (could you) use that (and maybe a globe valve) instead of circuit setters?
Hard to track down, but I purchased mine about a year ago from Hajoca, Salt Lake City (855) 982-1408; ask for Vern.
I considered those for my system but went with a single pressure gauge and two ball valves piped in parallel to the pumps. It decreases the margin of error which could be significant for residential applications.
Steve Minnich0 -
So for the circulator, you close one valve to read one side, and then switch it and read the other side?Steve Minnich said:I considered those for my system but went with a single pressure gauge and two ball valves piped in parallel to the pumps. It decreases the margin of error which could be significant for residential applications.
I'd be inclined to pipe the 2 taps to either side of something like a Dwyer differential pressure gauge of a low full scale but higher max pressure value so that you can calculate flow in systems with low resistance.
When I experimented with trying to measure flow with a single high precision gauge and a 3 way valve to toggle it between the inlet and the outlet of a balancing valve, I was never sure if I was really getting the differential or if the system pressure was fluctuating more than the differential across the valve.0 -
Or a simple Y hose across the two valves, with the single gauge.
I only have one valve to demo this
Yeah I like the idea of using something like that as a test instrument.Steve Minnich0
I did basically that. A pump probably has enough delta for that to work. When i did it across a balancing valve it was iffy if the variation was because of the differential across the valve or fluctuations in the pressure in the system at both points.0
- 50 Industry Classes
