Would You pipe this differently?
Timco
Timco Member Posts: 3,040
Oil boiler was here when we bought it. Got the EFTU free when I was at HTP and I just ran a gas main all the way across the house for LP in the kitchen and to equipment. The idea is to leave the oil system as a standby back up heat source. Throw a couple valves and a couple switches and you’re using one or the other. Same manifold. Due to where I threw the controls up I’m considering putting the new P/S manifold behind the oil boiler. Thoughts?
Just a guy running some pipes.
  • Ironman
    Ironman Member Posts: 7,851
    I can't exactly follow the piping from the pics, but I'd pipe both boilers injecting into the house loop through closely spaced Tees. I know it's an extra pump involved, but that way you'd only have to throw a switch to change over. Doing it like that, anyone (your wife family members, etc.) could do it without having to figure a valving arrangement.
    Bob Boan
  • Timco
    That’s exactly what I’m doing. There’s an internal pump in the wall unit and one for the oil boiler with 6 pumps not shown in the ceiling that run the zones.
    EBEBRATT-Ed Member Posts: 19,529
    I am a little concerned about the distance from the boiler to the oil tank. I think 5' is minimum
    STEVEusaPA
  • rick in Alaska
    rick in Alaska Member Posts: 1,513
    I am confused. Why is there a minimum distance from the tank? Is it a local code thing? Fire rating?
    Rick
    hot_rod Member Posts: 26,574
    Prime candidate for a HydroSep :)
    @rick in Alaska
    I know Mass code was always that the tank had to be 5' from the oil boiler. Mass has since dumped there Code and adopted NFPA.
    I am not sure what NFPA wants but I am sure there is some minimum distance.
    I realize the new boiler is gas but is installed between the oil boiler and the tank....looks pretty close.
    Just playing inspector here
  • rick in Alaska
    @rick in Alaska
    Thanks for the clarification. It makes sense where you are. I don't think about it because virtually all our tanks are outside on stands, so no where close to the burner.
    Rick
    @rick in Alaska
    I did look it up in NFPA-31 oil code and it is 5' tank to any source of ignition unlsee you put a 1 hour fire wall in between
    rick in Alaska
  • Timco
    So I was inspected today. Oil burner is 10’ and any other ignition source or appliance is 5’ or a 1-hour barrier. He’s asking me to hang some drywall but not secure it and that will suffice. Really nice guy. Passed my gas main.
    @rick in Alaska I did look it up in NFPA-31 oil code and it is 5' tank to any source of ignition unlsee you put a 1 hour fire wall in between
  • Ironman
    Is sealed combustion a "source of ignition"?
    Bob Boan
  • Timco
    The section says or any appliance. He was good about it.
    pecmsg Member Posts: 6,769
    That's a good question unfortunately the circs, t-stat and electrical box's on the HTP ARE a source of ignition!
  • Timco
    1) it’s not an electric water heater..
    2) the circ in this is Taco.
    Source of Ignition
    Electrical equipment is a source of ignition if it creates an arc or spark during operation.
    Cir maybe, maybe not. T-Stat YES!
    This is all up to the building inspector
    mattmia2 Member Posts: 15,547
    Us a thermistor and the boiler's control for the indirect. No switch on the water heater then...
    Do explosion proof switches with some sort of shielding still count as a source of ignition?