JLT1105 Member Posts: 1
Hi, We need to replace our condenser boiler. HVAC company is recommending either Navien NCB-240, or Williamson Power Vent -140,000BTU's. Anyone have information about these boilers?

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 23,162
    Well... without knowing what your heating load is, can't recommend anything. The HVAC company should have performed a Manual J study of your structure to determine the correct size boiler. Did they? What did it say?
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Ironman
    Ironman Member Posts: 7,367
    You also need to do a radiation survey to determine the output capacity of your emitters. It makes absolutely no sense to put in a boiler that has a higher output than the radiation (pick up factor excluded).
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • Ironman
    Ironman Member Posts: 7,367
    Can you post some pics of your current setup and its size. How about some basic construction data about you house? Its size, type of construction, year built, your locale?
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.