Boilers
JLT1105
Member Posts: 1
Hi, We need to replace our condenser boiler. HVAC company is recommending either Navien NCB-240, or Williamson Power Vent -140,000BTU's. Anyone have information about these boilers?
0
Comments
-
Well... without knowing what your heating load is, can't recommend anything. The HVAC company should have performed a Manual J study of your structure to determine the correct size boiler. Did they? What did it say?Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
You also need to do a radiation survey to determine the output capacity of your emitters. It makes absolutely no sense to put in a boiler that has a higher output than the radiation (pick up factor excluded).Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Can you post some pics of your current setup and its size. How about some basic construction data about you house? Its size, type of construction, year built, your locale?Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements