120 volt zone valve
Zman
Member Posts: 7,611
I am looking for some 1 1/2" and 1 1/4" 120 volt zone valves.
They would be simple N/C non modulating valves, no end switches needed. The 1 1/4" valves will have flow rates of 10-20 GPM, The 1 1/2" 28 GPM.
They are for garage unit heaters, if figure it is easier to wire in parallel with the fans than set a transformer and relay.
Albert Einstein
Albert Einstein
1
Can you use a solenoid valve. Don't know about the flow rates but sporlan would.0
Belimo
Honeywell
All make line voltage electronic valves.
There are line voltage ball valves as well
NO
NC
Spring Open
Spring closed0 -
I was hoping to find something in the zone valve price range."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Caleffi has an 1-1/4 Cv 7.5. That would handle the 10gpm
Wonder if properly piped you could parallel two. We do that with TMV and PRVsBob "hot rod" Rohr
Not my favorite ZV but these block head White Rogers have high Cv, add a transformer at the valve perhaps?Bob "hot rod" Rohr
Amazon has 110 Volt motorized 1 1/4" ball valves0
An xfmr and 2 parallel 1" valves like a taco zone sentry might be the least expensive and simplest option to get a high cv
It would be easier to mount a small xfmr in a knockout in the control or motor junction box and run tstat wire to the valve than to run flex to the valve anyhow.0 -
They're not "name brand" per se, but in the past I've used some of the 2" line voltage solenoid valves from electricsolenoidvalves.com and they've been great so far. If I remember correctly they're good for 30+ GPM, we've got them in on quite a few commercial feedwater systems. Price point is on par with a 24V zone valve0