120 volt zone valve
Zman
Zman Posts: 7,614
I am looking for some 1 1/2" and 1 1/4" 120 volt zone valves.
They would be simple N/C non modulating valves, no end switches needed. The 1 1/4" valves will have flow rates of 10-20 GPM, The 1 1/2" 28 GPM.
They are for garage unit heaters, if figure it is easier to wire in parallel with the fans than set a transformer and relay.
Albert Einstein
  • unclejohn
    unclejohn Posts: 1,833
    Can you use a solenoid valve. Don't know about the flow rates but sporlan would.
  • Zman
    Zman Posts: 7,614
    Do they make non refrigerant models?
    Albert Einstein
  • unclejohn
    Yes I have one for my beach house because my wife wouldn't crawl under to shut off the water it's only 3/4 " but I know they have larger pipe size.
    Zman
    pecmsg Posts: 7,485
    Belimo
    Honeywell
    All make line voltage electronic valves.
    There are line voltage ball valves as well
    NO
    NC
    Spring Open
    Spring closed
  • Zman
    Zman Posts: 7,614
    I was hoping to find something in the zone valve price range.
    Albert Einstein
    hot_rod Posts: 28,191
    Caleffi has an 1-1/4 Cv 7.5. That would handle the 10gpm
    Wonder if properly piped you could parallel two. We do that with TMV and PRVs
    Not my favorite ZV but these block head White Rogers have high Cv, add a transformer at the valve perhaps?
    pecmsg Posts: 7,485
    Amazon has 110 Volt motorized 1 1/4" ball valves
    mattmia2 Posts: 17,991
    An xfmr and 2 parallel 1" valves like a taco zone sentry might be the least expensive and simplest option to get a high cv
    It would be easier to mount a small xfmr in a knockout in the control or motor junction box and run tstat wire to the valve than to run flex to the valve anyhow.
  • GroundUp
    GroundUp Posts: 2,547
    They're not "name brand" per se, but in the past I've used some of the 2" line voltage solenoid valves from electricsolenoidvalves.com and they've been great so far. If I remember correctly they're good for 30+ GPM, we've got them in on quite a few commercial feedwater systems. Price point is on par with a 24V zone valve
  • Matt_67
    Matt_67 Posts: 316
    I think a Belimo B225+LF120 might be your best bet - CV of 30 and its a little more than a typical zone valve but its not bad. Pipe size is 1" so you could reduce to that. It looks like EnergyControl.com might be a good bet.
    Zman
  • Zman
    Zman Posts: 7,614
    @Matt_67, I think that is the best option, thank you.
    This building uses that Belimo valve with modulating actuators in other areas so the techs should be comfortable working on them.
    Albert Einstein