Drop Header
Looking at a steam job. The current boiler uses a drop header. Has 2 risers come up about 30” above water line. Then drop down to header which is about 16-18” above water line.
Seems to work but my understanding is header should remain 24” above water line? Or am I mistaken?
Thanks James
ranzerox
  • KC_Jones
    KC_Jones Member Posts: 5,933
    For a drop header the final height above the water line isn't as critical as a non drop header. In fact one of the advantages of the drop header is to get the header lower when there isn't much ceiling height to connect to the system.
    2014 Weil Mclain EG-40
    Jamie Hall Member Posts: 27,328
    What's important is that initial rise. Once it starts over and comes back down, all it has to be is above the water line in the boiler.
    STEAM DOCTORHap_Hazzard
    EBEBRATT-Ed Member Posts: 20,151
    @James Day_2
    What @Jamie Hall said is spot on. The header must be above the water line.
    Steamhead Member Posts: 18,469
    @James Day_2
    This.
    Consulting