Steam boiler repiping (photos)
Options
JStar
Posts: 2,752
I was initially contacted with complaints of water hammer, spitting vents, and uneven heating. After fixing the near boiler piping by adding a second boiler riser and a 3" drop header, all water hammer noises have been resolved.
The 10-20ft mains get hot within 3 minutes of making steam at the header, and the shorter main doesn't even have a main vent.
At startup, the boiler was producing over 5,000ppm CO, which we adjusted to below 100. No job is complete without a combustion analysis! Test it, or don't run it.
Our next follow up is to address a cold radiator and possibly some additional balancing.
Burnham 406B
The 10-20ft mains get hot within 3 minutes of making steam at the header, and the shorter main doesn't even have a main vent.
At startup, the boiler was producing over 5,000ppm CO, which we adjusted to below 100. No job is complete without a combustion analysis! Test it, or don't run it.
Our next follow up is to address a cold radiator and possibly some additional balancing.
Burnham 406B
3
Comments
-
Nice job!Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
@JStar Looks great. That boiler caught my eye since I've got a couple of them but smaller.
Do you know how old that boiler is? I don't know when Burnham stopped making the "4B" but mine are over 30 years old, and I figure they are on their last legs. Did you consider doing a complete replacement?
I am hoping, of course, they are long-lived. And while I don't have any water hammer, I do get kettling when the boilers start up, which I really don't like since I can feel the popping in the boiler risers before they get hot. (That's largely why I wonder how much time they have left.)0 -
@Chris_L , I've got a 4B also, a larger one (411B). It's 36 years old and going like the day it was installed. There are no guarantees but I think I'll likely get 40+ years out of this thing. They are built like tanks. I think they stopped making them around 1990, give or take a year.0
-
Looks like when that 406B needs replacement, the header configuration won't need more than very slight modification to be used with the replacement boiler. Nice work!
Co-Founder, All Steamed Up, Inc.
Baltimore, MD, USA
0 -
-
Keeping the new header "away" from the boiler and having some swing joints and unions makes installing a new boiler a lot easier when the time comes0
-
-
JStar, are you going to get back on Find a Contractor?
Co-Founder, All Steamed Up, Inc.
Baltimore, MD, USA
0 -
Maybe at some point. I'm not actively looking for side work, but I'll take it when someone finds me.0
Categories
- All Categories
- 87.8K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 430 Carbon Monoxide Awareness
- 129 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 123 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 79 Pipe Deterioration
- 1.1K Plumbing
- 6.6K Radiant Heating
- 396 Solar
- 16.1K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements