Steam boiler repiping (photos)
JStar
Member Posts: 2,752
I was initially contacted with complaints of water hammer, spitting vents, and uneven heating. After fixing the near boiler piping by adding a second boiler riser and a 3" drop header, all water hammer noises have been resolved.
The 10-20ft mains get hot within 3 minutes of making steam at the header, and the shorter main doesn't even have a main vent.
At startup, the boiler was producing over 5,000ppm CO, which we adjusted to below 100. No job is complete without a combustion analysis! Test it, or don't run it.
Our next follow up is to address a cold radiator and possibly some additional balancing.
Burnham 406B
The 10-20ft mains get hot within 3 minutes of making steam at the header, and the shorter main doesn't even have a main vent.
At startup, the boiler was producing over 5,000ppm CO, which we adjusted to below 100. No job is complete without a combustion analysis! Test it, or don't run it.
Our next follow up is to address a cold radiator and possibly some additional balancing.
Burnham 406B
3
Comments
-
Nice job!Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
@JStar Looks great. That boiler caught my eye since I've got a couple of them but smaller.
Do you know how old that boiler is? I don't know when Burnham stopped making the "4B" but mine are over 30 years old, and I figure they are on their last legs. Did you consider doing a complete replacement?
I am hoping, of course, they are long-lived. And while I don't have any water hammer, I do get kettling when the boilers start up, which I really don't like since I can feel the popping in the boiler risers before they get hot. (That's largely why I wonder how much time they have left.)0 -
@Chris_L , I've got a 4B also, a larger one (411B). It's 36 years old and going like the day it was installed. There are no guarantees but I think I'll likely get 40+ years out of this thing. They are built like tanks. I think they stopped making them around 1990, give or take a year.0
-
Looks like when that 406B needs replacement, the header configuration won't need more than very slight modification to be used with the replacement boiler. Nice work!All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
-
Keeping the new header "away" from the boiler and having some swing joints and unions makes installing a new boiler a lot easier when the time comes0
-
-
JStar, are you going to get back on Find a Contractor?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Maybe at some point. I'm not actively looking for side work, but I'll take it when someone finds me.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements