Emergency steam replacement
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......
Awesome job Dave! Do you carry all those fittings with you, or do you make a trip to the supply on your way there?
I have multiples of everything, mostly cast iron fittings except for some of the 3” fittings for the header. A job like this requires me bringing the big guns, the Ridgid 141 and stuff for pipe larger than 2”.ethicalpaul said:Awesome job Dave! Do you carry all those fittings with you, or do you make a trip to the supply on your way there?
DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
I cannot force people to spend money, I can only suggest how to spend it wisely.......1 -
Worked straight through, it’s the nature of the beast!!Intplm. said:Some very nice looking work there. And done in a emergency. Sixteen hours! Did you do this non-stop?
Looks great.DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
I cannot force people to spend money, I can only suggest how to spend it wisely.......3 -
Nice work Dave I remember the 16 hours days from my younger days now we only do 1/2 days 12 hours no more then lol great looking job keep it up Peace and good luck clammy
R.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
Specializing in steam and hydronic heating1 -
> @Dave0176 said:
> (Quote)
At least this time of year!NJ Steam Homeowner.
> @Dave0176 said:
> The old boiler was a Weil-McLain EG50 and they unfortunately had sprung a leak on the wet return, this time the LWCO probe had failed due to lack of maintenance.
Wait! You mean the Hartford Loop didn’t do its job??! 😅
Sorry I couldn’t resistNJ Steam Homeowner.
Actually Paul it did do its job of keeping water in the boiler, however with the low water cutoff inoperable there was nothing to shut down the burner, which in turn kept steaming off the water until it was bone dry.ethicalpaul said:> @Dave0176 said:
Sorry I couldn’t resistDL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
I cannot force people to spend money, I can only suggest how to spend it wisely.......0 -
Loop or not, 99% of the time the boiler will eventually dry fire anyway because no one pays attention until the house is cold.
I'd say the Hartford Loop's job is to prevent dry fire but I've been known to have odd opinions
Could you tell from the condition of the pipes (or maybe you had a chance during your install to see it) how fast was the wet return leak? Did it go right down the drain, or did it pool on the floor and they saw it?
And sorry for all the questions, but this topic interests me for some reason: How did they discover the failure? Did the dry fire cause smoke?
If you're too busy to answer I totally understand, I'll ask you about it next time I see youNJ Steam Homeowner.
I imagine when the boiler ran out of water to make steam with, the house started getting cold.ethicalpaul said:How did they discover the failure? Did the dry fire cause smoke?
Not sure about that this time of year and during a heat cycle. It must not take very long for a dry fire situation to turn ugly. There's no control to stop it, right? I wonder if it starts to make strange sounds.Hap_Hazzard said:
It would take a few cycles to go from the level of the Hartford loop to bone dry, and I imagine it might make some interesting noises. Maybe when the sections started getting red-hot the jacket started flexing and buckling.Just another DIYer | King of Prussia, PA
I don't think it would necessarily take a few cycles, but even if it did, the boiler would keep generating heat and working fine until the water just about ran out so only the last cycle really matters (I say never having tried it).
@ethicalpaul
The HO told me they were aware of the return pipe leak because it had been going off on low water. Apparently the leak got bigger and unfortunately the last instance the probe failed to sense the low water. She said she began to notice a smell of “fire” and called the fire dept. When they show up they noticed the boiler dry firing and shut it down. She said we’re going to try and use a pipe clamp to stop the leak temporarily, however it was too late. We’re actually going back in the spring to replace the entire wet return.
@Hap_Hazzard
Since it was a Weil-McLain it basically just burned up the return gaskets, I could not find any visible cracks in the boiler sections
Thanks @Dave0176 sounds like she acted fast and was very fortunate. Don't ignore those leaks, folks!
Forty years ago I notice a "hot smell" in my back hall one summer day. so I went down the basement to see what was going on. The landlord had divided the basement with a wood wall with a doorway so you could access his side for the fusebox, etc.
Everything seemed fine on my side but I could see a red glow on the other side of the wall. I went through and saw a large red spot on the back of his old Delco steam boiler. I killed the power and the boiler shut down, 5-10 minutes later a heard a load crack and that was the end of that old boiler.
This was in 1979 and those 30-40 year old boilers did not have a LWCO safety on them. The boiler was used for hot water as well as steam so I assume it fired up to heat the domestic hot water.
3PSI gauge1
- 87.1K THE MAIN WALL
- 58 Biomass
- 114 Chimneys & Flues
- 110 Geothermal
- 163 Indoor-Air Quality
- 71 Pipe Deterioration
- 999 Plumbing
- 393 Solar
- 55 Water Quality
- 46 Industry Classes
