VR8304m Gas valve inop
How can I test it ? I have power and grd. And no pilot light lit
    Alan (California Radiant) Forbes Member Posts: 4,699
    edited November 2019
    Check to see if you are getting 24 volts at the following terminals:
    PV
    MV/PV
    If yes, you need a new gas valve. If no, you may need a new ignition control module OR some component in the safety string is open (spill switch, flame-rollout switch, flue damper........).
    If you are not familiar with the components, get a professional in there.
    Steamhead Member Posts: 18,411
    THIS!
    @happysenior , where are you located?
    Consulting
    Jolly Bodger
  • Tim McElwain
    Tim McElwain Member Posts: 4,660
    Do you have gas to the unit? Simple question but that is the best place to start. When you say you have power 24 volts of 120 volts. That valve is a 24 volt valve by the way.