VR8304m Gas valve inop

Options
How can I test it ? I have power and grd. And no pilot light lit

Comments

  • Alan (California Radiant) Forbes
    edited November 2019
    Check to see if you are getting 24 volts at the following terminals:
    PV
    MV/PV
    If yes, you need a new gas valve. If no, you may need a new ignition control module OR some component in the safety string is open (spill switch, flame-rollout switch, flue damper........).

    If you are not familiar with the components, get a professional in there.
    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
  • Steamhead
    Steamhead Posts: 18,910

    If you are not familiar with the components, get a professional in there.

    THIS!

    @happysenior , where are you located?

    Co-Founder, All Steamed Up, Inc.

    Semi-retired

    Baltimore, MD, USA

    Jolly Bodger
  • Do you have gas to the unit? Simple question but that is the best place to start. When you say you have power 24 volts of 120 volts. That valve is a 24 volt valve by the way.