VR8304m Gas valve inop

How can I test it ? I have power and grd. And no pilot light lit

Comments

  • Alan (California Radiant) Forbes
    Alan (California Radiant) Forbes Member Posts: 4,214
    edited November 2019
    Check to see if you are getting 24 volts at the following terminals:
    PV
    MV/PV
    If yes, you need a new gas valve. If no, you may need a new ignition control module OR some component in the safety string is open (spill switch, flame-rollout switch, flue damper........).

    If you are not familiar with the components, get a professional in there.
    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
  • Steamhead
    Steamhead Member Posts: 17,380

    If you are not familiar with the components, get a professional in there.

    THIS!

    @happysenior , where are you located?
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    Jolly Bodger
  • Tim McElwain
    Tim McElwain Member Posts: 4,642
    Do you have gas to the unit? Simple question but that is the best place to start. When you say you have power 24 volts of 120 volts. That valve is a 24 volt valve by the way.