Another steamer install
EzzyT
Member Posts: 1,379
We ripped out the old oil fired boiler and Indirect and installed a Peerless Ect-04 with a Carlin EZGas Burner and a HTP indirect tank with Caleffi TankMixer Valve.
Still have to go back to finish installing the Fan in Can.
1
Nice and tight!
Great install as usual.Never stop learning.0 -
As always Ezzy at the top of the heap ,can’t say much more except ETDFW meaning ezzy Travis does fine work ,great spinning my friend never a need to say keep up the great work you always do .peace and good luck clammy
R.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
Very nice install ! Beautiful drop header. And the full size pig tail setup. Less of a chance of that 1/4 inch bent pipe getting clogged.
One suggestion is to add an isolation valve between the feed into the boiler and the drain on the dry return. Give you the option to steam clean the system without any dirty water making it back to the boiler. But with a dry return I'm sure the system is pretty clean as is.0 -
I forgot to add this picture into which we did last year. Loop seal and upgraded main venting.
Before the loop seal both dry returns tied in together at the height of the drops and also tied into one common dry return.
Between the pitch of the common dry return which one can see at the boiler we wouldn’t get our Dimension A, so the loop seal was the best option to overcome that issue.
Thanks @clammy & @Ron Jr._3
And yes that dry return is just condensation from the overflow of the loop seal.0 -
Wow. Nice clean job in a very tight location. Looks great.0
Top Notch. Perfection.
I assume it was oil? What the B&G loop doing, some basement hydronics?There was an error rendering this rich post.
@STEVEusaPA thanks.
The old boiler was a Weil 68 series steamer.
The B&G pump is for the indirect hot water tank.0 -
Beautiful install that should last decades.
You didn’t list out the B&G 100 pump. 2x the cost of other options but those things can last 40 years of more if maintained. It costs half as much as the indirect tank. I assume it’s main advantage is the motor is external so not cooled by the oxygenated and contaminated boiler water.0 -
Remind us what efficiency numbers you see when steaming and during DHW production. I figured it approaches 86% for DHW, maybe 87% if “flooded” in the summer and temp turned down to maybe 160. Just curious.0
Excellent work as always.Bob Boan
@mikeg2015 @Ironman thanks. The efficiency combustion numbers are the same during a heating & dhw cycles.0
Beautiful install Ezz and I like the EC boiler.DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0
- 120 Geothermal
