I'm have a 45x30 foot Morton building and am redoing my 2 zone radiant heat system. The water heater that I used died the other day so I am putting in a wall hung boiler and new manifolds and lines. I've spent some time looking on the internet for some new layout ideas but they all seem so complicated. The simplest one I found is the picture below but even it has several bends and routing that don't make sense to me. Looking at the hot water line out why is the cold water return connected to it at that tee? Then why make the 90 degree drop, to the left of the air separator, only to come back up to the pumps then turn around and go down again? Why not just run straight across to the pumps? And the same for the cold water return lines, why not just go straight across to the boiler instead to going up over the pressure tank then down again? Also what is the pump for on the cold water return? I apologize for all the questions but it just seem so complicated?
Thanks,
Jack
Thanks,
Jack
That is piped primary/secondary. They did it that way because they needed to have one flow rate to allow for adequate flow through the boiler. The flow to the zones will vary depending on which zones are calling.
Most boiler manufactures recommend that design in their I&O manual"If you can't explain it simply, you don't understand it well enough"
Albert Einstein3 -
Thank you for your reply. So is that a shared line for both output (hot) and return (cold)? And what does the pump do on the return (cold) line?
Jack0 -
The pump on the cold line circulates water through the boiler. The other pumps circulate water through the system. Through the miracle of modern physics, the system pumps & the boiler pump can run independently without significantly effecting each other. Get yourself a copy of Pumping Away, it explains it in a very accessible way.
There's also various issues of idronics to read, which will help you understand—although they are quite a bit more technical in nature.
In short, the picture you showed is about as simple as things can get using modern practices & equipment. After you read Pumping Away it will all make sense, after tou read through some of the idronics issues you'll be able to tell if another piping arrangement might suite you better,1 -
Sure they could have straightened it out a bit. Maybe they didn't realize you can rotate the circulator motor or they thought a heat trap would be advantageous. Overall the picture in your example is how a system like that should be piped."If you can't explain it simply, you don't understand it well enough"
Albert Einstein1 -
Don't think of it as hot and cold, think of it as 2 loops with different flow rates.JackW said:Thank you for your reply. So is that a shared line for both output (hot) and return (cold)? And what does the pump do on the return (cold) line?
Jack"If you can't explain it simply, you don't understand it well enough"
Albert Einstein1 -
What are the two fixtures on the top line on either side of the air separator? The other fixture looks like a pressure release valve. Looks like there is one on the return side also.0
Looks like that is where they are filling/purging the system. There is a ball valve there so they close it off during the filling process, hook a hose to one of the boiler drains to fill and a hose to the other boiler drain to let out the air through out the purging process.
Yes the other item is a pressure relief, I personally would like that closer to the boiler on the outlet side.
D1 -
Ratio thanks for the book recommendation, ordered it this morning from Amazon.0
Is there a one way valve before the cold water circulation pump? If not what prevents cold water from being pulled into the hot water stream from hot water pump instead of going to the boiler?0
DeZoro it looks like they have a pressure valve right at the hot water outlet so isn't it odd that they would put another one that far away from the boiler?0
I agree. I posted this earlier but didn't get any answers, do you know if there a one way valve before the cold water circulation pump? If not what prevents cold water from being pulled into the hot water stream from instead of going to the boiler to be reheated?0
DeZoro is there any reason I couldn't use an inline check valves?0
DZoro I looked into them and will be getting three new pumps, thanks.0